    Refrigeration discharging



    I have a heat pump that seems to fluctuating in wildly in the refrigeration circuit.A technician has told me that it is down to poor flow/air in the heating distribution side,and that this is the cause for the refrigeration discharging ,he said this happens when pockets of air travel through the condensor and the refrigerant has no water to work with.The unit is a biggy ( 88kw).Would it not go out on low//high pressure though first?

    Does anyone agree/disagree with this engineer?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Refrigeration discharging

    It would help us all if you were to post the type and model of your system.

    As we do not have the benefit of seeing your system, we have to rely on you to be our eyes and ears.

    My crystal ball broke some time ago

  3. #3
    Join Date
    Nov 2009
    Location
    United kingdom
    Age
    51
    Posts
    5
    Rep Power
    0

    Re: Refrigeration discharging

    It is a thoren ground source heat pump,hope this helps?

  4. #4
    Join Date
    Nov 2009
    Location
    United kingdom
    Age
    51
    Posts
    5
    Rep Power
    0

    Re: Refrigeration discharging

    It is a thoren ground source heat pump 88kw ,twin copeland scroll compressor,hope this helps.

  5. #5
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Refrigeration discharging

    Judging by what u say it should be a water-water heat pump, but how bad dose it fluctuate.

    some amount of fluctuation might be possible because of what u say with the air, but u should hear the sound of it judging by 88 Kw, u should have a large amount of water passing in the unit, sou sound clearly should be heard, and see on the water pressure gage.
    And it could be possible to not trip the pressure switch's at the beginning.
    But u should solve your problem with the air

    but it's important what fluctuation do u have

  6. #6
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Refrigeration discharging

    refrigeration discharging
    Please explain

  7. #7
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Refrigeration discharging

    I'm lost...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  8. #8
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Refrigeration discharging

    Quote Originally Posted by desA View Post
    I'm lost...
    you are not lost , we know where u are, you are here


  9. #9
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Refrigeration discharging

    If your water loop is full of air, then flow will be poor and possibly be speradic, this will cause your discharge pressure to rise and fall.
    Surely the first issue is to get rid of the air! Add a simple air release valve(s) at your highest points. Ensure the whole system is always at positive pressure (not just at the pump outlet)