    Your Comments on the selection?



    Can you pl. comment on the selection of the receiver?
    Attached Files Attached Files



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Your Comments on the selection?

    Don't know what your local regulations require , but your calculations indicate that you want to store all liquid in plant .
    That is a good thing but most systems this would be a luxury .
    What situation would you have to pump out everything ?

  3. #3
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    867
    Rep Power
    26

    Re: Your Comments on the selection?

    Quote Originally Posted by RANGER1 View Post
    What situation would you have to pump out everything ?
    Many plants I have worked on are seasonal, and shut down in the winter. We would pump them all back in the winter time.
    I would doubt that where I live you would get a Engineer to put his stamp on the plans if the receiver would not not hold all the charge and be less than 80% full.
    That is not to say that many plants have not been added to over time and the receiver will not hold the entire charge. I have had to deal with this many times.
    Another situation that could arise is if you shut down and have no place cool to keep the liquid. In warm areas you can blow a relief on the low side if you try to leave refrigerant in the evaps.

  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Your Comments on the selection?

    Yes the Plant operation is seasonal & hence the receiver has to take care of all the liquid. Am I considering extra safety as such?

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Your Comments on the selection?

    We are in a different climate than most.
    I would say that all plants I work on never shut down .
    Plate freezer plants with 20-30 tonne of ammonia , rely on low side accumulator as main liquid storage tank .
    Cool stores never shut down either .

    I agree with reciever being correct size whenever possible .
    Last edited by RANGER1; 07-11-2009 at 09:02 AM.

Similar Threads

  1. Help with chiller selection - 200 > 300 KW
    By ec225 in forum Commercial
    Replies: 5
    Last Post: 29-08-2009, 07:02 AM
  2. selection and sizing
    By MIT in forum Technical Discussions
    Replies: 2
    Last Post: 22-06-2009, 11:27 PM
  3. TX Valve Selection: PHT or TE
    By JERRYCOOL in forum Industrial
    Replies: 6
    Last Post: 05-08-2008, 02:10 AM
  4. Replies: 3
    Last Post: 19-02-2007, 05:22 PM
  5. selection of centrifugal fan
    By watana in forum Air Conditioning
    Replies: 0
    Last Post: 14-09-2003, 04:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •