    Cooling in humid climate without reheat - possible?



    Hi,

    I am wondering whether it is possible to do a cooling for ambient 30 +/- 5 C and 75 +/- 5% RH to a room temperature of 24 +/- 2 C and 60 - 70% RH?

    Thanks.



  2. #2
    Join Date
    Nov 2009
    Location
    Singapore
    Posts
    5
    Rep Power
    0

    Re: Cooling in humid climate without reheat - possible?

    Oops, I mean cooling with just cooling coil and without reheat.

    Thanks.

  3. #3
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Cooling in humid climate without reheat - possible?

    Cooling and de humidification is feasible in Humid climate.
    Madras in southern India which is around 35 degree c and 70% RH ambient is cooled to 24 RH not exceeding 60%.No reeat is used.

  4. #4
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Cooling in humid climate without reheat - possible?

    All the Window air conditioners made to the best of knowledge is only cooling

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Ferumbras View Post
    Oops, I mean cooling with just cooling coil and without reheat.

    Thanks.
    Yes it is. You need to control sensible to latent heat ratio by varying air quantity across evaporator or by controlling cooling capacity of refrigerant system.

  6. #6
    Join Date
    Nov 2009
    Location
    Singapore
    Posts
    5
    Rep Power
    0

    Re: Cooling in humid climate without reheat - possible?

    That sounds good. What's the strategy used?

    I have seen a place that runs chilled water with chilled water supply at 17 C, out at 19 C but the humidity is still around 70% with temperature at 21.5 C. When the temperature setting was increased to 23.5 C, we have 97% RH measured at the sensor.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Ferumbras View Post
    That sounds good. What's the strategy used?

    I have seen a place that runs chilled water with chilled water supply at 17 C, out at 19 C but the humidity is still around 70% with temperature at 21.5 C. When the temperature setting was increased to 23.5 C, we have 97% RH measured at the sensor.
    Here is simplest solution I could give from my head right now.

    Room termostat controls compressor ON-OFF and room hygrostat controls two speed fan.

    When set room temperature is reached compressor goes OFF. When set room temperature plus differential is reached compressor goes ON.
    When set room humidity plus differential is reached, fan switch to lower speed (if compressor is ON). When set room humidity is reached fan switch to high speed (regardless of compressor ON-OFF condition).
    Last edited by nike123; 06-11-2009 at 11:41 AM.

  8. #8
    Join Date
    Nov 2009
    Location
    Singapore
    Posts
    5
    Rep Power
    0

    Re: Cooling in humid climate without reheat - possible?

    The case I am faced now is pure thermostat control. Single speed fan running at 3,740 CMH. That is the bad news.

    In addition, the original design is with steam heating coil and steam humidifier. I am thinking that those 2 things are pretty much in the way and cost a fortune. That's why I am wondering whether it is entirely possible for the design to run purely on cooling coil. Problem is that I don't know the temperature of air leaving the cooling coil. A test setting room at 20.5 C seem to get humidity 70% without problem but 23.5 C setting results in over 90% RH, I suspect because at 30 C, 70% RH, the dew point is 24 C.

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Ferumbras View Post
    The case I am faced now is pure thermostat control. Single speed fan running at 3,740 CMH. That is the bad news.

    In addition, the original design is with steam heating coil and steam humidifier. I am thinking that those 2 things are pretty much in the way and cost a fortune. That's why I am wondering whether it is entirely possible for the design to run purely on cooling coil. Problem is that I don't know the temperature of air leaving the cooling coil. A test setting room at 20.5 C seem to get humidity 70% without problem but 23.5 C setting results in over 90% RH, I suspect because at 30 C, 70% RH, the dew point is 24 C.
    It is still possible to use room humidity-stat and some fan speed controller which can be bypassed with humidity-stat when humidity in room is at set value.

  10. #10
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: Cooling in humid climate without reheat - possible?

    make sure the fan is cycking off when the compressor is not running...

    having the fan run without compressor makes people feel good but will push humidity back into the room as not all the water runs off of the coil....
    -Christopher

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Cooling in humid climate without reheat - possible?

    In order to achieve the desired humidity the coil must be cold enough to remove the moisture and the system must run long enough to do the job.

    Reheat does not remove moisture, it extends run time.

    In order to reach 50% humidity, the temperature of the air leaving the coil needs to be at least 11K lower than the room temperature.

    You can adjust the temperature of the air leaving the coil by adjusting the fan speed.

  12. #12
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Ferumbras View Post
    Hi,

    I am wondering whether it is possible to do a cooling for ambient 30 +/- 5 C and 75 +/- 5% RH to a room temperature of 24 +/- 2 C and 60 - 70% RH?

    Thanks.
    If the question is can a cooling cool by itself take 30C air at 75% and give you a supply air stream (air leaving the coil ) of 24 C and 65% RH the answer is no, it needs reheat. There is no apparatus dew point, it is impossible

    Can a coil take that warm humid outside air and maintain a room at 24C and 65% RH without reheat, the answer is yes
    Take the V out of HVAC and you are left with a HAC job

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Abby Normal View Post
    If the question is can a cooling cool by itself take 30C air at 75% and give you a supply air stream (air leaving the coil ) of 24 C and 65% RH the answer is no, it needs reheat.
    Or a heat pipe/run around loop?

  14. #14
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Gary View Post
    Or a heat pipe/run around loop?
    perhaps, may need more reheat than a passive system can do though

    you have to cool the air until it has the dewpoint you want, then reheat it to get the 24C
    Take the V out of HVAC and you are left with a HAC job

  15. #15
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Gary View Post
    Or a heat pipe/run around loop?
    Interesting thought. Can you explain further?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  16. #16
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by desA View Post
    Interesting thought. Can you explain further?
    The old runaround loop consisted of two water coils. One was placed before the evaporator and one after the evaporator. Water was pumped from one coil to the other and back in an endless loop.

    The precoil cooled the air before it entered the evaporator, thus the evaporator ran at a lower temperature, increasing dehumidification.

    The heat absorbed by the precoil was transferred back to the airstream by the postcoil, thus reheating the air.

    The modern version of this is the heatpipe, which contains refrigerant. The refrigerant boils in the warmer coil and condenses in the cooler coil, for the same effect... without the pump. It relies entirely upon temperature difference and gravity.

  17. #17
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Cooling in humid climate without reheat - possible?

    ^ Thanks Gary.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  18. #18
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Cooling in humid climate without reheat - possible?

    The problem is the supply chilled water temperature, at +17 'C leaving at +19 'C , the latent cooling/ moisture removal/ dehumidification will be next to zero. So you get half reasonable dry buld and high humidity in control space.
    More water chiller capacity required.
    As Gary suggested the supply chilled water temp should be in region of 10 > 12 'C, then sensible heat ratios start to get realistic, and dehumidification happens, if a budget design system it may not happen.
    Check the fresh air make up volume, may be way to high.

  19. #19
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Cooling in humid climate without reheat - possible?

    The assumption here is that we are cooling 100% outdoor air.

    Is that what the question is about or are we talking about recirculated air?

  20. #20
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Cooling in humid climate without reheat - possible?

    Indeed, how
    ambient 30 +/- 5 C and 75 +/- 5% RH
    conditioned to the
    23.5 C setting results in over 90% RH,
    ?!

  21. #21
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Yuri B. View Post
    Indeed, how

    conditioned to the

    ?!
    Maybe there is some mixing with indoor air. Or measuring instrument cannot measure more than 90% RH.
    Last edited by nike123; 08-11-2009 at 08:37 AM.

  22. #22
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Cooling in humid climate without reheat - possible?

    Or a humidifier is working, the poster unawares of it, still as far as he even
    don't know the temperature of air leaving the cooling coil

  23. #23
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Yuri B. View Post
    Or a humidifier is working, the poster unawares of it, still as far as he even
    Wet bulb temperature (dew point) of air 30°C and 75%RH is 25°C. That mean that, by cooling that air to 25.1C, we should see 100%RH.
    As you see, in this case, there is no need for humidifier.
    And from posted data it is visible that we have some air mixing with drier/hotter air (probably recirculation).
    Last edited by nike123; 08-11-2009 at 11:05 AM.

  24. #24
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Ferumbras View Post
    The case I am faced now is pure thermostat control. Single speed fan running at 3,740 CMH. That is the bad news.

    In addition, the original design is with steam heating coil and steam humidifier. I am thinking that those 2 things are pretty much in the way and cost a fortune. That's why I am wondering whether it is entirely possible for the design to run purely on cooling coil. Problem is that I don't know the temperature of air leaving the cooling coil. A test setting room at 20.5 C seem to get humidity 70% without problem but 23.5 C setting results in over 90% RH, I suspect because at 30 C, 70% RH, the dew point is 24 C.

    For 30°C and 75%RH of outdoor air of volume of 3740 CMH to cool to 23,5°C and 60%RH you need at coil 37KW of cooling capacity. (29kW latent and 8kW sensible).

    What is capacity of your chiller (if I understand correctly that chiller is cooling water)?
    Also, is it all 3740 CMH fresh air or part is recirculated.

    Usual temperature of chiller water is 7°C flow/ 12°C return.
    Why is your such high?

  25. #25
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Ferumbras View Post
    The case I am faced now is pure thermostat control. Single speed fan running at 3,740 CMH. That is the bad news.

    In addition, the original design is with steam heating coil and steam humidifier. I am thinking that those 2 things are pretty much in the way and cost a fortune. That's why I am wondering whether it is entirely possible for the design to run purely on cooling coil. Problem is that I don't know the temperature of air leaving the cooling coil. A test setting room at 20.5 C seem to get humidity 70% without problem but 23.5 C setting results in over 90% RH, I suspect because at 30 C, 70% RH, the dew point is 24 C.
    You have to cool the air down until it has a lower dew point than what you want to maintain in the room.

    But the problem seems to be that the room will get too cold if you do this.

    So you have two options.

    Once the room has fallen to the temperature that you want, keep running the cooling but reheat the supply air up to room temperature, this keeps the dehumidification going without over cooling the room.

    The second option is to add an independent dehumidifier.

    A cooling coil alone will not work for you in this case.

    I am in a humid region myself. I have to use reheat under about 3 different certain conditions.

    1) When there is a high amount of outside air.

    2) When I am forced to use a high air volume for filtration purposes such as a clean room or operating theatre

    3) When there is a high latent load, due to a high concentration of people in the space. It is worse when the people are active like a night club, an aerobics class or a Pentacostal Church

    My favourite solution involves free reheat either passive or hot gas because our deisel generated electricity is so expensive here

    Here is a unit I had that was custom built, chilled water coil will cool mixed air down to 52 to 54 F range (11.1 to 12.2) and because of the high moisture content in the outdoor air here, the air off of the chilled water coil will be fog. The space dew point tends to drive towards the temperature off of the chilled water coil.

    The fan and motor will reheat this air by 3F (1.7C) there is a lot of static on the system.

    When it needs further dehumidification a DX coil engages and pulls the air down to 48F (8.9C)

    At the same time, the condneser coil for this DX reheats the air. When combined with the fan and motor heat it blows 65F dry air (18.3F)

    Basically a room thermostat turns on the DX dehuimidifier and reheat. A room dehumidistat does the same. I have to keep the rooms at 20C or 68F. I am actually monitoring the return air stream, not using room stats

    Coil section you can see the upstream chilled water connections, the brown coil in the front is the DX condenser coil, there is a DX evap coil in between. The brown is heresite and anti-corrosion coating there is salt in the outdoor air here



    Compressor compartment inside of the coil section, has hot gas bypass can keep the space under 40% RH if need be



    Blower comparetment, BAF fan and premium efficiency motor



    Moves 9000 CFM (15291 CMH) of which 2150 CFM (3653 CMH) is outside air warmer and more humid than the original poster was talking about
    Last edited by Abby Normal; 08-11-2009 at 02:37 PM.
    Take the V out of HVAC and you are left with a HAC job

  26. #26
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Cooling in humid climate without reheat - possible?

    it produces about 1700 litres of condensate per day
    Take the V out of HVAC and you are left with a HAC job

  27. #27
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Cooling in humid climate without reheat - possible?

    here is an all DX version I did in 2002 for a night club

    Main 8 row coil used four DX stages to pull mixed air down to 52F, on demand a 4 ton secondary DX coil was used and the condenser for the 4 ton circuit reheated the air. When combined with some fan heat it blew 64F (18C) dry air



    When you use humid air, you do not have to cool it much to turn it into fog, the dry bulb and wet bulb off of a coil will be pretty much equal.

    A red flag telling you that you need reheat will be that you calculate that the supply dry bulb and wet bulb are relatively far apart like more than 1.5C
    Take the V out of HVAC and you are left with a HAC job

  28. #28
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Cooling in humid climate without reheat - possible?

    For those of you concerned about CFM per Ton, the DX version in the post above was about 150 CFM a ton
    Take the V out of HVAC and you are left with a HAC job

  29. #29
    Join Date
    Oct 2006
    Location
    Lima Peru
    Age
    54
    Posts
    19
    Rep Power
    0

    Re: Cooling in humid climate without reheat - possible?

    Quote Originally Posted by Abby Normal View Post
    For those of you concerned about CFM per Ton, the DX version in the post above was about 150 CFM a ton
    Abby, you describe an industrial dehumidifier, I believe that this system needs low energy to control of humity (in front other systems) but how it controls the temperature with other conditions of the year? you include the sensible heat of the condenser the rest of the year too. .. thank you in advanced

Similar Threads

  1. Energy saving Glycol filled dry cooler circuits
    By Jasper in forum Technical Discussions
    Replies: 14
    Last Post: 19-06-2008, 02:18 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •