    Temperature difference in chamber (test question)



    Hi all.

    I am working on assignment and ive had a question like this -

    "You have been sent to a local Health Authority, whose drugs storage cabinet is not performing to specification. You have monitored the temperature across the chambers and the variance is between +4 degrees at the top to -3 degrees at the bottom.

    Write a memo to your manager stating your findings and reccommending an appropriate solution to rectify the fault"
    ****
    Ok guys, heres my questions:
    What is potentially causing this temp variation as mentioned above, in the storage cabinet?
    As appropriate, then, how can this be rectified?

    Im thinking it something probmlematic with the evap fans or there is stock in the way of the unit. Please could you throw some lengthy answers into this!

    Thank you
    Best regards
    Copple



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Temperature difference in chamber (test question)

    Copple,
    definitly a trick question. Limited information given so requires multi-options reply, and some lateral thinking required. ( That is what they want to here, thinking outside the circle, the obvious ).
    1/ is it a dual temp cabinet with static coil in cooler section. Answer possible insulation between freezer and cooler faulty so freezing product in lower section of chiller area.
    2/ is it a single cabinet with forced air from top to bottom through a plenum, them probable product restriction freezing bottom area.
    options are endless, look observe, think , and then report possible problem.
    magoo

  3. #3
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: Temperature difference in chamber (test question)

    I feel following possibility :

    1. Evap. is of static type that too its bottom freezer, hence bottom is -3 and Top is +4 ,
    2. There is a problem of air flow means its completely blocking the return air path, means all the cooling is getting stored in Bottom
    3. Fan of the evap. got stuck hence cooling but not uniform.
    4. Excess ice formation on the evap. leading towards no air circulation across the eva, hence bottom side excess cooled, top side warm.

    Thanks
    amit

  4. #4
    Join Date
    Aug 2008
    Location
    England
    Age
    38
    Posts
    21
    Rep Power
    0

    Re: Temperature difference in chamber (test question)

    Thanks guys, great responses. I will consider your points very closely when answering the question.

    Best regards
    Copple

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Temperature difference in chamber (test question)

    Write a memo to your manager stating your findings and reccommending an appropriate solution to rectify the fault.
    The answer that will get you the least brownie points is:-

    "The temperatures are uneven although the product storage method is correct. There could be an airflow problem, which I favour, but I would suggest that we call a reputable refrigeration engineer quickly before we lose any of the product."

    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Aug 2008
    Location
    England
    Age
    38
    Posts
    21
    Rep Power
    0

    Re: Temperature difference in chamber (test question)

    Quote Originally Posted by Brian_UK View Post
    The answer that will get you the least brownie points is:-

    "The temperatures are uneven although the product storage method is correct. There could be an airflow problem, which I favour, but I would suggest that we call a reputable refrigeration engineer quickly before we lose any of the product."


    This worked well, thank you.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Wrong temperature on control panel
    By swee'pea in forum Trouble Shooting
    Replies: 2
    Last Post: 14-01-2009, 09:18 AM
  3. CTC advance micro featrure and comparison
    By absolute-zero in forum Transport
    Replies: 0
    Last Post: 06-12-2007, 08:53 PM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •