Results 1 to 5 of 5
Thread: Chiller expansion tank.
-
04-11-2009, 01:29 AM #1
Chiller expansion tank.
Hello,
I am looking for help sizing an expansion tank for a chilled water system. It is an exsisting system and I don't know exact fluid content. Do I need to do a dilution test to get a accurate messurement. Can I just overestimate?
-
04-11-2009, 02:34 AM #2
Re: Chiller expansion tank.
Expansion tank shall be kept at topmost level of the chilled water circuit.ideally it is better to calculate the total holding capacity of circuit .As a rule of thumb around 3% of the flow rate is adequate for expansion tank if it is chilled water system
-
04-11-2009, 08:21 PM #3
Re: Chiller expansion tank.
Document here has tables and calculations for sized expansion vessels.
http://www.mikrofill.com/images/PDF/n-and-de-range.pdfBrian - Newton Abbot, Devon, UK
Retired March 2015
-
05-11-2009, 08:17 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Chiller expansion tank.
Here is software for such calculations.
-
16-11-2009, 01:27 AM #5
Re: Chiller expansion tank.
THANKS Guys knew you could help
Similar Threads
-
design of expansion tank
By scherif in forum Technical DiscussionsReplies: 8Last Post: 24-08-2010, 11:24 PM -
Expansion Of Tank
By bibin777 in forum FundamentalsReplies: 1Last Post: 08-07-2009, 06:20 PM -
Open expansion tank pipe size
By A_Ahed in forum Air ConditioningReplies: 0Last Post: 18-04-2009, 01:14 PM -
How an expansion tank works?
By Raadster in forum FundamentalsReplies: 6Last Post: 25-07-2008, 02:25 PM -
water expansion tank
By Lc_shi in forum Air ConditioningReplies: 5Last Post: 30-01-2005, 11:49 PM