  1. #1
    Davmarr's Avatar
    Davmarr Guest

    Airedale Fault



    HI
    Anyone help, been looking at an airedale ACC 120 D chiller 2 comps 4 stage. unit runs ok then "faults" the comps unload and shut down, as they are doing this the fault clears and it all starts up again run for a bit and faults again. No indication on the Trend panel what the alarm is , all running pressurs are ok when its running. The prob is its just not telling us the fault is.



  2. #2
    Join Date
    Sep 2007
    Location
    UK
    Age
    60
    Posts
    45
    Rep Power
    0

    Re: Airedale Fault

    Is this chiller controlled from a BMS system, if so are the run request signal cables healthy?

    Pavilion

  3. #3
    MTX's Avatar
    MTX Guest

    Re: Airedale Fault

    The only fault that I have had on these chillers that dont show as a fault are oil pressure. Also check the control protocol is it in local on/off?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Airedale Fault

    As MTX says, check the control strategy.

    Some controls will ramp up and down in percentage points. The cooling could get turned ON at say 65% of signal.

    The temperature then changes slightly and the signal drops to 62% and the cooling is turned OFF again.

    This is the worst type of control for compressor operation. You need a wide deadband to ensure that the compressors get a decent run time.

    I've lost two compressors before due to that type of control.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Daikin r407c 2 pipe vrv ja fault code any offers?
    By Contactor in forum Air Conditioning
    Replies: 11
    Last Post: 28-07-2009, 01:26 AM
  2. Fault with Tango cassette
    By airefresco in forum Air Conditioning
    Replies: 8
    Last Post: 19-09-2007, 08:42 AM
  3. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM
  4. Fault on an Airedale unit
    By marc5180 in forum Air Conditioning
    Replies: 50
    Last Post: 30-06-2007, 06:10 PM
  5. lg fridge/freezer fault light on function display board
    By bazza in forum Trouble Shooting
    Replies: 0
    Last Post: 25-02-2007, 04:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •