03-11-2009, 12:47 PM #1
Airedale Fault
HI
Anyone help, been looking at an airedale ACC 120 D chiller 2 comps 4 stage. unit runs ok then "faults" the comps unload and shut down, as they are doing this the fault clears and it all starts up again run for a bit and faults again. No indication on the Trend panel what the alarm is , all running pressurs are ok when its running. The prob is its just not telling us the fault is.
-
09-11-2009, 08:01 PM #2
Re: Airedale Fault
Is this chiller controlled from a BMS system, if so are the run request signal cables healthy?
Pavilion
-
10-11-2010, 06:29 PM #3
Re: Airedale Fault
The only fault that I have had on these chillers that dont show as a fault are oil pressure. Also check the control protocol is it in local on/off?
-
10-11-2010, 08:54 PM #4
Re: Airedale Fault
As MTX says, check the control strategy.
Some controls will ramp up and down in percentage points. The cooling could get turned ON at say 65% of signal.
The temperature then changes slightly and the signal drops to 62% and the cooling is turned OFF again.
This is the worst type of control for compressor operation. You need a wide deadband to ensure that the compressors get a decent run time.
I've lost two compressors before due to that type of control.Brian - Newton Abbot, Devon, UK
Retired March 2015
Similar Threads
-
Daikin r407c 2 pipe vrv ja fault code any offers?
By Contactor in forum Air ConditioningReplies: 11Last Post: 28-07-2009, 01:26 AM -
Fault with Tango cassette
By airefresco in forum Air ConditioningReplies: 8Last Post: 19-09-2007, 08:42 AM -
UA Daikin Fault Code
By jedi in forum Air ConditioningReplies: 2Last Post: 23-07-2007, 01:44 PM -
Fault on an Airedale unit
By marc5180 in forum Air ConditioningReplies: 50Last Post: 30-06-2007, 06:10 PM -
lg fridge/freezer fault light on function display board
By bazza in forum Trouble ShootingReplies: 0Last Post: 25-02-2007, 03:25 PM