    dear all...

    please guide me to select a fan for a ventilation system.ie. fan selection,static pressure,rpm,cfm calcuations...etc

    regards/kathir



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: ventilation and fan selections

    As a wise gentleman from your country stated some years ago....

    For designing an Air Handling Unit, you should first have to design the Coil size. The next thing is to select the proper fan. If you are proposing to manufacture AHU then you got to have a knowledge on the same. Otherwise there are a lot many AHU manufacturers in our country. You can get a lot of good informations from the web site shown below.
    http://www.swegon.com/

    Click on resources.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: ventilation and fan selections

    what is the application? It depneds on the load or heat to be removed or air changes required then only the fan selection will come.
    Standard way is to arrive at the air quantity and the components like Fan transformation, filter, intake lovers, cooling coil, ducting registers etc which come in air distribution circuit.
    Every companent will have resistance against the air quantity which are summed up to get the total static required.

  4. #4
    ahmed eltaweel's Avatar
    ahmed eltaweel Guest

    Re: ventilation and fan selections

    brain_uk sir
    i'm pleased to know you sir

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: ventilation and fan selections

    Quote Originally Posted by ahmed eltaweel View Post
    brain_uk sir
    i'm pleased to know you sir
    And you also Ahmed,
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: ventilation and fan selections

    Quote Originally Posted by kathir View Post
    dear all...

    please guide me to select a fan for a ventilation system.ie. fan selection,static pressure,rpm,cfm calcuations...etc

    regards/kathir
    I don't know if the best book on air side design is still in print but do try and locate a copy of "WOODS practical guide to fan engineering", it will not matter if it is OLD fan laws do not change.
    The definition of a fan is a "machine which propels air continuously by aerodynamic action"
    There are three basic types of fans, centrifugal, propeller and axial.
    All three are selected for different types of applications the major selection criteria being external resistance, noise etc.
    Fan Laws.
    With constant impeller size
    1. Volume flow varies directly as speed of rotation
    2. Pressure developed varies as (speed of rotation)2
    3. bhp absorbed varies as (speed of rotation)3

    With constant speed of rotation
    4. Volume flow varies a (impeller size)3
    5. Pressure developed varies as (impeller size)2
    6. bhp absorbed varies as (impeller size)5

    Consequently with varying speed of rotation and impeller size
    7. Volume flow varies as (speed of rotation) x (impeller size)3
    8. Pressure developed varies as (speed of rotation)2 x (impeller size)2
    9. bhp absorbed varies as (speed of rotation)2 x (impeller size)5

    I am sorry that the system does not allow the (squared 2) or the (cubed 3) etc. to be put in the correct location ie against the bracket above the base line.

    To answer your original question, first you have to determine the air volume required to ventilate the space under consideration. The next phase of selection requires a calculation of the air distribution system, ductwork, grilles, diffusers etc. to provide an assessment of the anticipated external resistance to air flow the fan will have to over come to deliver the calculated air volume.
    The type of fan would be selected based on the type of application, for example an axial 2 pole would be acceptable in an industrial application but due to the noise generated a centrifugal would be more appropriate for commercial and residential ventilation systems.

    I hope some of this helps.

  7. #7
    Join Date
    Oct 2009
    Location
    india
    Posts
    6
    Rep Power
    0

    Re: ventilation and fan selections

    thanks for the replies..

  8. #8
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    78
    Posts
    195
    Rep Power
    17

    Re: ventilation and fan selections

    The Woods guide to fan engineering is here for free.

    There is also a beautiful noise control book there as well.
    Last edited by Frikkie; 11-11-2009 at 10:09 PM. Reason: Forgotten something

  9. #9
    Join Date
    Oct 2009
    Location
    india
    Posts
    6
    Rep Power
    0

    Re: ventilation and fan selections

    can anybody help me for vrf piping design?

  10. #10
    Join Date
    Oct 2009
    Location
    india
    Posts
    6
    Rep Power
    0

    Re: ventilation and fan selections

    hi...can anybody help me out for design of vrf piping?

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: ventilation and fan selections

    Quote Originally Posted by kathir View Post
    hi...can anybody help me out for design of vrf piping?
    Refer to the manufacturers installation instructions or design book.