    Chiller Machine Ambient Problem



    Hi guys! We have a litle problem in our chiller machine. According to manufacturing, it can operate at the maximum ambient temp of 48°C but we are exceeding more than 55°C in summer causing the machine to stop at high pressure alarm. We tried supporting it with dessert cooler and it worked for sometime.Can somebody advise me for long time solution? Thanks!



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Chiller Machine Ambient Problem

    hi crash + burns, have you got an air cooled or is it water cooled?=

  3. #3
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Chiller Machine Ambient Problem

    Quote Originally Posted by sedgy View Post
    hi crash + burns, have you got an air cooled or is it water cooled?=
    Umm 'ambient' suggests air...

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Chiller Machine Ambient Problem

    Yes, there is a simple solution,
    You can either change the condenser to a bigger one, about 50% larger, or add another one to the existing condenser.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Chiller Machine Ambient Problem

    Quote Originally Posted by Crash & Burns View Post
    Hi guys! We have a litle problem in our chiller machine. According to manufacturing, it can operate at the maximum ambient temp of 48°C but we are exceeding more than 55°C in summer causing the machine to stop at high pressure alarm. We tried supporting it with dessert cooler and it worked for sometime.Can somebody advise me for long time solution? Thanks!
    What refrigerant is in the system and at what pressure does it stop at high pressure alarm?

  6. #6
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Chiller Machine Ambient Problem

    Quote Originally Posted by crash & burns View Post
    hi guys! We have a litle problem in our chiller machine. According to manufacturing, it can operate at the maximum ambient temp of 48°c but we are exceeding more than 55°c in summer causing the machine to stop at high pressure alarm. We tried supporting it with dessert cooler and it worked for sometime.can somebody advise me for long time solution? Thanks!
    hi if your unit is on a roof of a complex and u have exhust fanes u can point the ductes twards the condenser in order to use the lower temp air to cool your condenser but this is a very limited solution not for a long term ,
    changing condenser to a bigger one is very expensive but would solve problem termanaly!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  7. #7
    Join Date
    Jun 2004
    Location
    Scotland
    Age
    56
    Posts
    12
    Rep Power
    0

    Re: Chiller Machine Ambient Problem

    Oldest solution that works sit a hose on the condenser and let water run over it nothing removes heat like evaporation its how a fridge works - think its called latent heat. Of course you do need water and that may be costly, also pooling warm water does breed disease - but if the 55 deg is temporary it will work ie only some days during summer. Other than that the right thing to do is fit a condenser that will handle the duty ie a bigger one or as suggested a second one. Only other thing I can offer is the condenser in direct sunlight cause solar gain can push a system over the edge where it may work in shade.

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  2. Replies: 2
    Last Post: 29-05-2009, 12:30 AM
  3. Chiller connectivity problem
    By ALLAHHOOPK in forum New Technologies
    Replies: 2
    Last Post: 12-05-2009, 05:57 PM
  4. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Replies: 5
    Last Post: 07-03-2008, 05:13 AM
  5. neslab chiller water pump problem
    By bill0577 in forum Trouble Shooting
    Replies: 5
    Last Post: 19-10-2006, 05:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •