    Head pressure control method.



    I fully understand the need for head pressure control. (not that I always agree with the need in all applications)
    The question is: In the USA they seem to control with a valve, do you also control fan speed or fan cycling or do you just let them run?
    In NZ as general rule (has some exceptions) we control the air flow, and do not use valves.



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: Head pressure control method.

    mad fridgie , are you talking evaporative condensors or something else ?
    Are you saying you use method of fan speed ie VFD ?

  3. #3
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Head pressure control method.

    Quote Originally Posted by RANGER1 View Post
    mad fridgie , are you talking evaporative condensors or something else ?
    Are you saying you use method of fan speed ie VFD ?
    Sorry for not making clear, Air cooled condensors (dry) DX systems, Controlling the air either VSD (larger systems) Phase cutting (smaller systems) staging the fans (medium to large but on the cheap most common!)

  4. #4
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Head pressure control method.

    The air cooled condenser fans shall be linked to the air quantity required and ambient or discharge pressure. In many cases the compressor starts after the discharge pressure is increased fan comes on that too in stages.

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Head pressure control method.

    Mad Fridgie.
    Been there done that so to speak. Tried step control on pressure, total erratic control of discharge pressure.
    So currently have systems on base load fans continous based minimum loading and VLT control and the balance, but have compatible motors to suit. Straight line pressure control not totally acheivable, but close. As in Christchurch area I would consider a discharge regulation PM vav to maintain discharge condition on compressor and be wide open for summer, with VLT control from there on. Add an ORIT vav to add pressure to receiver for liquid flow to system at low ambients or partial loads.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Head pressure control method.

    I think the use of the head pressure control valve depends on how cold it actually gets. Variable speed operation might be acceptable down to some specific temperature. However, if the ambient drops real low you might still need the head pressure control valve to block of condensing surface to maintain the discharge pressure.

    In these conditions a balanced port TXV is more forgiving than an unbalanced port.
    Last edited by US Iceman; 29-10-2009 at 07:19 PM. Reason: obviously can't spell...
    If all else fails, ask for help.


  7. #7
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Head pressure control method.

    I agree with all , thanks.
    So in USA if you had for example 60Kw (cooling) stand alone air cooled refrigeration unit lets say SST -8C, would it be standard practice to install a head pressure control valve?, DO you also control the condensor fans or do you just LEAVE them running?

  8. #8
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Head pressure control method.

    Quote Originally Posted by US Iceman View Post
    Ithiunk the use of the head pressure control valve depends on how cold it actually gets. Variable speed operation might be acceptable down to some specific temperature. However, if the ambient drops real low you might still need the head pressure control valve to block of condensing surface to maintain the discharge pressure.

    In these conditions a balanced port TXV is more forgiving than an unbalanced port.
    I also like the idea of the double port valves (small and large port), never actually seen one in use. I believe sporlan makes these products.

  9. #9
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: Head pressure control method.

    most all of the systems i work on large and small have either variable speed condensor fans or have fan cyclers on them... in fact a lot of manufacturers "low ambient kit" is nothing more than a fan cycling switch.. then again ive only ever worked on domestic space conditioning and not coolers or refrigerators...

    in my case there;s always been enough heat transfer at the evaporator to keep the head pressure up at the condensor with simply cycling the fans...
    -Christopher

  10. #10
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Head pressure control method.

    Hi there,

    As said by the others, using head pressure valve depends on ambient temperature. If it does not get so cold during winter them fan cycling/speed control is enough.
    You can check it during winter: cycle the fans and then see if discharge pressure still decreases then you need valve.
    Using head pressure control valve needs careful design and charging otherwise, you will have more problems than before.
    Cheers
    Even Einstein Asked Questions

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Head pressure control method.

    Fan cycling is far more common... even when I was up in Michigan where it gets very cold.

    That said, I have worked on a few flooded condenser systems. They are a pain in the butt.
    Last edited by Gary; 29-10-2009 at 04:36 AM.

  12. #12
    Join Date
    May 2009
    Location
    china
    Posts
    18
    Rep Power
    0

    Re: Head pressure control method.

    I experienced a 12kW system with fan cycling scheme not working stable, Its hard to simulate the same condition in Lab, but in field at certain circumstance, it's easy to trigger LP switch, even when the ambient isn't too low. for lower ambient trying a accumulator with a heater working togather with a solinoid valve is Ok. Fan should be working on low speed.

  13. #13
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Head pressure control method.

    Quote Originally Posted by mad fridgie View Post
    I also like the idea of the double port valves (small and large port), never actually seen one in use. I believe sporlan makes these products.
    Yeah, they are great. If I have to use a TXV, I always try to use a Sporlan balanced port valve. They are more forgiving than the others IMHO.
    If all else fails, ask for help.


  14. #14
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Head pressure control method.

    Flooded condenser with head pressure control valves can be a pain in the butt to charge. That's for sure. You have to charge them according to the lowest anticipated ambient temperature or they won't have sufficient refrigerant to flood the condenser coil. Then in the summer you have to make sure the receiver is large enough to hold the excess liquid.

    I've seen some cold weather in Southern Indiana where fan cycling would not work at all.
    If all else fails, ask for help.


  15. #15
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Head pressure control method.

    I have found that is the condensor coil is vertical, than fan control works well enough, but if you have a horizontal coil, then fan control is less efficient at controlling (natural convection being the problem)

  16. #16
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Head pressure control method.

    Quote Originally Posted by mad fridgie View Post
    I have found that is the condensor coil is vertical, than fan control works well enough, but if you have a horizontal coil, then fan control is less efficient at controlling (natural convection being the problem)
    That's interesting. I never saw too many vertical coils when I pulled wrenches for a living to say one way or the other.

    The flip side to what you saw though is: in that sense, a vertical coil would have more surface area of the coil exposed to the wind too, which could make control more difficult?
    If all else fails, ask for help.


  17. #17
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Head pressure control method.

    Quote Originally Posted by US Iceman View Post
    That's interesting. I never saw too many vertical coils when I pulled wrenches for a living to say one way or the other.

    The flip side to what you saw though is: in that sense, a vertical coil would have more surface area of the coil exposed to the wind too, which could make control more difficult?
    It may be In NZ (very small population and a long way from anywhere) we tend to build condensing units in a Kit form, reduced amount of stock required (common size condensors) So if we have a larger duty we may stack a couple or more condensors on top of each other.
    Wind here is not a problem as far temperature goes (If it is winding, and it gets windy then temperatures are not normally that cold) We get low ambients when the air is still

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. Low head pressure Versus Heat reclaim.
    By taz24 in forum Supermarket Refrigeration
    Replies: 17
    Last Post: 20-03-2008, 11:47 AM
  4. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  5. Replies: 10
    Last Post: 11-12-2007, 09:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •