Results 1 to 9 of 9
    Dec 2004
    Weihai,China
    800
    aluminum heat exchanger
    hi sirs
    Is it feasible to apply aluminum tube for evaporative condenser if it's with good anti-corrosion?
    It's cheaper than copper and lighter than steel.
    what's your comment?
    thx!
    rgds
    LC
    Mar 2009
    KZN, South Africa
    64
    2,212
    Re: aluminum heat exchanger
    Quote Originally Posted by Lc_shi View Post
    hi sirs
    What is an 'evaporative condenser'?
    Sep 2003
    ISRAEL
    72
    4,248
    Aluminium will have to be coated against corrosion.
    Jan 2008
    India
    70
    171
    Aluminum as such is not protected from corrossion as we seen complete fins got powdered with three months of installation at Salallah in Oman.
    Thus if it aluminum alloy with corrosion protection should be suitable.
    Mar 2009
    KZN, South Africa
    64
    2,212
    Quote Originally Posted by Sridhar1312 View Post
    If aluminium is used correctly, the aluminium oxide layer is generally sufficient to protect the fin material. The corrosion mechanism here is the speed with which the fin forms its protective oxide layer.
    What messes things up is if the aluminium is sacrificial with respect to some other material e.g. copper - or even aluminium-alloy, in the presence of water. This forms a galvanic corrosion cell.
    The way to assist here could be suitable fin protection (coating), suitable resistant alloy, or even correct electrical earth-straps - some form of disrupting the electrical galvanic cell.
    My main concern is aluminium-copper systems in the presence of stray current & water, which would accelerate the corrosion cell.
    Aluminium-aluminium fin-tube systems can be made to last for reasonable lifetimes under fairly extreme operating conditions. Look at the condenser & radiator in most modern automobiles.
    Dec 2008
    China
    87
    Very good! desA.
    I have studied the corrosin mechannism of the aluminium and the aluminium-copper heat exchanger. I found that aluminium will corroded if it was with copper by the mechanism of electrical galvanic corrosion.
    Mar 2009
    KZN, South Africa
    64
    2,212
    ^ Thank you. It is my pleasure.
    If you need further information in this field, please ask - I'll try to point you in the right direction.
    Dec 2004
    Weihai,China
    800
    Hi desA
    Your comment is valuable. I plan to try to build a AL coil as an evaporative condenser. There're two issues need be considered:
    #1 : the water is sprayed on the AL coil ,how about the corrosion ?
    #2: need to weld aluminum with copper tube of the compressor. how about the electriacl corrosion between copper and al
    Mar 2009
    KZN, South Africa
    64
    2,212
    What materials eg. 3003, 6000x series etc, are you using for the fins, tubes? You will need to investigate their galvanic potential values - by test - AFTER brazing. If mechanically-joined, then the as-supplied galvanic potentials.
    Use an aluminium tube clad with copper. This is now common in Asia.
    If galvanic corrosion of the pipe/compressor joint becomes a problem, then perhaps look into an electrical strap across the pipe/compressor joints, to remove charge build-up.
    There are electrical devices which can also disrupt a galvanic corrosion cell. Be careful of stray electrical currents.
  1. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  2. Basics or is it?
    By Fett in forum Fundamentals
    Last Post: 10-09-2009, 01:45 AM
  3. frostles heat pump
  4. heat exchanger for small chiller
    By star882 in forum Fundamentals
    Last Post: 30-01-2007, 12:06 PM
  5. R134a <-> liquid heat exchanger design
    Last Post: 10-05-2002, 08:36 AM