    two stage verses economized single stage



    I am presently installing a economized single stage system for R717 with a -28 deg. F suction. I am calculating about a 4% electrical operating penalty verses two stage, with lower initial capital as the offset. What do others think about this approach.



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: two stage verses economized single stage

    Frigoscandia ( They now have a new name ) do it all the time and they are considered a leader in spiral freezing food products .
    Depends probably on how big plant is for this "4%" to be feasable .

    If its only 1 compresor and maybe a small holding one as well it would be feasable .
    Of course only screw comps could be used for the duty you propose .

  3. #3
    Clarkson's Avatar
    Clarkson Guest

    Re: two stage verses economized single stage

    Yes I am using screw compressors and I am also running them at > 90% of there capacity on a steady state load.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: two stage verses economized single stage

    It comes down to capital outlay versus savings, what is design capacity and operating design conditions.

  5. #5
    Clarkson's Avatar
    Clarkson Guest

    Re: two stage verses economized single stage

    My design conditions are for 87 deg. F condensing, -28 deg. F suction at a 400 Ton load using two fully loaded compressors. My load is full or nothing, which is why I leaned towards the lower capital cost of installation. This seems like a perfect application.

  6. #6
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: two stage verses economized single stage

    Earlier with R12 we have done comfortable single stage installations without any issues. Now with what refrigerant it is planned. According to me on certain low temperature applications it is the functional need which supercedes the cost or power.

  7. #7
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: two stage verses economized single stage

    Quote Originally Posted by Clarkson View Post
    Yes I am using screw compressors and I am also running them at > 90% of there capacity on a steady state load.
    Make sure that this is real 90% capacity. Sometimes slide valve indicator shows 90% but real capacity is 50-60%. Efficiency of single stage compressor with economizer will drop to efficiency of single stage compressor at 70-80% of compressor capacity(real).

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: two stage verses economized single stage

    Segei brings up a good point here. Slide valve position provided by the indication (display or dial gauge) is not equal to the same percentage of capacity.

    Depending on the compressor the 90% indicated could be just enough to cause the compressor to be operating where the side port is uncovered. This can affect the economizer (will need back-pressure regulators to maintain the economizer temperature/pressure).

    The slide valve position can drastically affect the part load performance also. It may not be just 4% penalty. It could be more as it depends on the actual capacity developed by the compressor at the indicated slide position and the resulting power input.
    If all else fails, ask for help.


  9. #9
    Clarkson's Avatar
    Clarkson Guest

    Re: two stage verses economized single stage

    Iceman,

    I like the back pressure valve idea.

    Thanks

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: two stage verses economized single stage

    Quote Originally Posted by Clarkson View Post
    Iceman,

    I like the back pressure valve idea.

    Thanks
    Well... don't laugh but I've seen people use economized screws with a flash tank and no BPR to control the flash tank pressure. When the screw unloads the liquid feed pressure goes to suction pressure.

    Glad to help...
    If all else fails, ask for help.


  11. #11
    Join Date
    Jul 2005
    Location
    SOMEWHERE IN THE PLANET
    Age
    46
    Posts
    67
    Rep Power
    19

    Re: two stage verses economized single stage

    Quote Originally Posted by US Iceman View Post
    Well... don't laugh but I've seen people use economized screws with a flash tank and no BPR to control the flash tank pressure. When the screw unloads the liquid feed pressure goes to suction pressure.

    Glad to help...
    Yes. It calls 'floated condition'. And it looks like this method could give better performance from York's software.

Similar Threads

  1. Single stage refrigeration system optimizing diagram
    By autt in forum System Optimization
    Replies: 34
    Last Post: 03-12-2008, 04:13 PM
  2. Replies: 7
    Last Post: 13-12-2007, 07:31 PM
  3. Single compression vs two stage compression.
    By Pawel_Wisnik in forum Technical Discussions
    Replies: 0
    Last Post: 07-09-2007, 01:53 PM
  4. Single stage Vs 2 stage comp rack
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 0
    Last Post: 01-02-2007, 04:05 PM
  5. single stage screw compressor
    By murugan in forum Trouble Shooting
    Replies: 0
    Last Post: 18-05-2006, 01:27 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •