two stage verses economized single stage
I am presently installing a economized single stage system for R717 with a -28 deg. F suction. I am calculating about a 4% electrical operating penalty verses two stage, with lower initial capital as the offset. What do others think about this approach.
-
26-10-2009, 07:34 PM #2
Re: two stage verses economized single stage
Frigoscandia ( They now have a new name ) do it all the time and they are considered a leader in spiral freezing food products .
Depends probably on how big plant is for this "4%" to be feasable .
If its only 1 compresor and maybe a small holding one as well it would be feasable .
Of course only screw comps could be used for the duty you propose .
-
26-10-2009, 10:04 PM #3
Re: two stage verses economized single stage
Yes I am using screw compressors and I am also running them at > 90% of there capacity on a steady state load.
-
26-10-2009, 10:37 PM #4
Re: two stage verses economized single stage
It comes down to capital outlay versus savings, what is design capacity and operating design conditions.
-
27-10-2009, 12:03 AM #5
Re: two stage verses economized single stage
My design conditions are for 87 deg. F condensing, -28 deg. F suction at a 400 Ton load using two fully loaded compressors. My load is full or nothing, which is why I leaned towards the lower capital cost of installation. This seems like a perfect application.
-
27-10-2009, 11:55 AM #6
Re: two stage verses economized single stage
Earlier with R12 we have done comfortable single stage installations without any issues. Now with what refrigerant it is planned. According to me on certain low temperature applications it is the functional need which supercedes the cost or power.
-
27-10-2009, 03:29 PM #7
Re: two stage verses economized single stage
-
27-10-2009, 05:40 PM #8
Re: two stage verses economized single stage
Segei brings up a good point here. Slide valve position provided by the indication (display or dial gauge) is not equal to the same percentage of capacity.
Depending on the compressor the 90% indicated could be just enough to cause the compressor to be operating where the side port is uncovered. This can affect the economizer (will need back-pressure regulators to maintain the economizer temperature/pressure).
The slide valve position can drastically affect the part load performance also. It may not be just 4% penalty. It could be more as it depends on the actual capacity developed by the compressor at the indicated slide position and the resulting power input.If all else fails, ask for help.
-
29-10-2009, 07:36 PM #9
Re: two stage verses economized single stage
Iceman,
I like the back pressure valve idea.
Thanks
-
29-10-2009, 07:42 PM #10
Re: two stage verses economized single stage
If all else fails, ask for help.
-
07-11-2009, 01:05 PM #11
Similar Threads
-
Single stage refrigeration system optimizing diagram
By autt in forum System OptimizationReplies: 34Last Post: 03-12-2008, 03:13 PM -
Different between compressor MYCOM single stage and compressor booster
By thien nhat in forum CommercialReplies: 7Last Post: 13-12-2007, 06:31 PM -
Single compression vs two stage compression.
By Pawel_Wisnik in forum Technical DiscussionsReplies: 0Last Post: 07-09-2007, 01:53 PM -
Single stage Vs 2 stage comp rack
By Kevin Yeo in forum Supermarket RefrigerationReplies: 0Last Post: 01-02-2007, 03:05 PM -
single stage screw compressor
By murugan in forum Trouble ShootingReplies: 0Last Post: 18-05-2006, 01:27 PM