    Problems with AHUs



    Hi all, would appreciate if anyone can help solve my queries.

    Currently, i have got a AHU located near to my Kitchen Exhaust Fan. And i have receive complaint from the tenant that the room (whereby the AHU supply air to) is giving out strong food odour, and i have actually closed up my outside air intake (fresh air damper = 0%), leaving with supply air intake flow = return air intake flow. However even using this method, the smell still surfaced. Could using of HEPA filter solve my problem? Please advise.

    Thank You.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Problems with AHUs

    Hi Terthong.
    Your extract system requires fat separation filters that require cleaning daily, as well carbon filters to absorb as much adour as possible after the fat separation filters.They can or should be cleaned daily as well, and replaced regularly.
    Hepa filters will block totally in a few hours, so disregard them.

  3. #3
    Join Date
    Jun 2002
    Location
    Mumbai, India
    Age
    66
    Posts
    25
    Rep Power
    0

    Re: Problems with AHUs

    Hi,
    You may have closed the fresh air intake of the AHU but the AHUs are not leak tight. So it may be absorbing some air discharged by the kitchen exhaust fan.

    A permanent solution is to relocate the AHU.
    If this is not possible, seal all joints of the AHU with a good quality silicon sealant to prevent air ingress in the AHU.

  4. #4
    Join Date
    Sep 2005
    Location
    Granard, Ireland
    Age
    55
    Posts
    43
    Rep Power
    0

    Re: Problems with AHUs

    Hello terthong
    Try puting an duct extension on your kitchen exhaust away from the AHU fresh intake or an extra duct on the freshair intake of the AHU to take fresh air further away from the kitchen exhaust fan.

    Fixit
    FIXIT............first time every time

Similar Threads

  1. Oil problems with a dual temperature pack.
    By Chunk in forum Supermarket Refrigeration
    Replies: 33
    Last Post: 11-09-2008, 03:29 AM
  2. samsung rs21dcns problems
    By slovenian ian in forum Trouble Shooting
    Replies: 2
    Last Post: 03-11-2007, 03:19 AM
  3. Oversized Liquid Recievers?? Problems??
    By nickjh in forum Fundamentals
    Replies: 12
    Last Post: 12-06-2007, 07:54 AM
  4. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM
  5. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Replies: 1
    Last Post: 16-07-2002, 02:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •