Results 1 to 8 of 8
21-10-2009, 09:41 PM #1
Using compressor as a vacuum pump to pull vacuums
Hi recently an apprentice I was working with used the compressor to pull the unit into a vacuum. He closed off the discharge service valve, removed the cap tube off it, cracked open the suction valve and connected his suction gauge on, he then ran the compressor and it pulled into a vacuum, once he finished doing that, always in a hurry he then forgot about the discharge side being closed, put the cap tube back on and charged unit with 60psi of liquid R404a and then tried to run it Very strange noises occurred after that, the compressor makes a half hearted effort to start, almost like it doesnt have enough power to run it, and then it trips the CB and is quite warm on the outer casing. Please Help
21-10-2009, 09:45 PM #2
Re: Using compressor as a vacuum pump to pull vacuums
Buy a new compressor!
21-10-2009, 09:55 PM #3
Based on what you have said and assuming all the service valves are in the correct position for running, it sounds like the compressor is siezed, would have been cheaper to use a proper vacuum pump even if in meant buying one....
Of course its possible its not wired up properly also.
21-10-2009, 09:55 PM #4
If my boss does, he's probably gonna buy another apprentice too and throw the old one out with the old compressor. I was told that too much liquid probably would have caused the compression of liquid in the shaft causing a locked rotor, causing the unit to trip, he suggested i reclaim all the 404 and leave valves open for a couple of hours, would that work
21-10-2009, 09:56 PM #5
21-10-2009, 09:59 PM #6
21-10-2009, 10:00 PM #7
21-10-2009, 10:10 PM #8
OK, if you are lucky, and it was completely full of liquid, there maybe a chance that no rotation occured, you simply overloaded the motor. So open up your valves, heat the crankcase (this will boil off any liquid, no point F****** any futher) Do not reclaim yet. When warm, restart! If it work great (as far as reclaiming yes this should be done, vacuum with a vac pump, recharge with NEW refrigerant, destroy old refrigerant), if not "well".
The apprentice not his fault, he is the apprentice, and unfortunatly this is part of the learning curve, you show me some one who has not f*** up in this industry, I will show you a liar!!!!
Vacuum Pump Questions
By position1 in forum FundamentalsReplies: 7Last Post: 08-10-2009, 02:33 AM -
Vacuum cleaner as a vacuum pump
By chemi-cool in forum Chit Chat & Service StoriesReplies: 18Last Post: 14-08-2009, 10:11 PM -
vacuum reduces when vac pump is isolated
By bill1983 in forum FundamentalsReplies: 40Last Post: 04-08-2009, 08:00 AM -
Troubleshooting a vacuum pump and gauge set.
By Old Codger in forum FundamentalsReplies: 7Last Post: 08-08-2008, 05:13 PM -
inverters pulling vacuum
By bangoman in forum Air ConditioningReplies: 2Last Post: 05-02-2008, 09:12 PM