    Argh! 507 system charged with 404A... expected problems?



    Ive got a multideck thats been charged with 404A after a compressor change. have just found out that origional manufacture used 507 in the system.

    Its been working fine for the last 3 weeks now, but can i expect any probelms? Different oils? Different charges?


    Cheers!



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Argh! 507 system charged with 404A... expected problems?

    The oils will be the same, i think R404A is R507 with a bit of R134a mixed in. R404A txv's are marked up to work with R507 as well. So my money would be on ok, but i don't know for sure

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Argh! 507 system charged with 404A... expected problems?

    Quote Originally Posted by monkey spanners View Post
    The oils will be the same, i think R404A is R507 with a bit of R134a mixed in. R404A txv's are marked up to work with R507 as well. So my money would be on ok, but i don't know for sure
    Exactly so. The two refrigerants are almost identical.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Argh! 507 system charged with 404A... expected problems?

    Confirmed.

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Argh! 507 system charged with 404A... expected problems?

    No problems. The properties of this gas mix will be in the middle of R507 and R404A, and this two blends have almost the same composition and properties.
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    Jun 2009
    Location
    East Anglia
    Age
    38
    Posts
    204
    Rep Power
    15

    Re: Argh! 507 system charged with 404A... expected problems?

    Phew!

    Thanks very much for so many good replies!

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. how do i know my system is charged well
    By duraid in forum Fundamentals
    Replies: 19
    Last Post: 29-09-2005, 07:27 PM
  5. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 04:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •