    Hi,

    I have a condensing Temp. of 30 DEG C with an absolute pressure of 14 bar, and a Evaporating Temp. of 5 DEG C with an absolute pressure of 5 bar.

    I need to work out the superheat values i.e. Sd10 and Hd10 so I can work out the value of Hd.

    Does anyone have any advice where i can obtain these values from as i am struggling.

    Many thanks

    Nikki



  2. #2
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: R22 Superheat Values.

    Are you sure they are absolute pressures?

    If they are you have problems with your evaporator.
    Tony

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: R22 Superheat Values.

    Don't know what Sd10 or Hd10 are but if you have your refrigerant pressure/temperature charts the answers will be there.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  4. Replies: 12
    Last Post: 14-07-2008, 03:00 PM
  5. Superheat
    By shogun7 in forum Fundamentals
    Replies: 24
    Last Post: 23-08-2004, 05:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •