    Absorption Fridges



    Hi all, my first post.

    Have been doing lots of work on my caravan fridge. Have got the venting right, added a thermally controlled fan and finally a close tolerance electronic thermostat.

    I know find out that the thermostat is not working out the way I thought it would. It would appear as if the heating and cooling cycle of the absorbtion fridge is such that once the element is switched on it takes a time for the ammonia to heat and therefore there is a rise in fridge temperature whilst this is happening. This is creating fluctuations that make the fridge less accurate than what I would like.

    There appear to the novice a couple of ways around this;
    1.) I thought of having a permanent heat source keeping the ammonia safely below boiling point. This will be done through PWM control keeping the voltage lower than full mains. Then having the thermostat kick in to do the top up buy applying full voltage to the element. This should greatly reduce the response time.

    2.) As the controller is 100 times more accurate and better able to control was to increase the heater wattage.

    Is this possible, is it dangerous, am i barking up the wrong tree?

    Cheers
    Andrew



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Absorption Fridges

    Welcome to the forum Andrew.

    My first thought would be that you are barking up that tree.

    Small fridges such as yours are not designed for, or mechanically able, close control.

    I would like to be proved wrong however so will wait for those more knowledgeable than me on these little beasties.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Absorption Fridges

    Absorbtion systems are slow reacting as you have gathered, why do not install a PID controller to directly control the element (may need electronic switching device) I suspect it may take a few cycles to stabalise.
    I presume this is not just for your beer, but for storage of medical bits and pieces.
    If I remember rightly you do not have a fan inside, so trying to keep a constant soley on natural convection is near on impossible, (an average can be obtained over time)

  4. #4
    Join Date
    Oct 2009
    Location
    South Africa
    Age
    63
    Posts
    11
    Rep Power
    0

    Re: Absorption Fridges

    Thanks boys,

    I have made progress, originally the fridge was fitted with the old capilliary tube thermostat arrangement and that was giving about a 14.5°C range in fridge temperature. I am now down to about 3 or 4°C (but in ambients of 33°C).

    The problem is that we camp in areas that can have large ambient temperature swings, this means the controller setting for daytime 45°C freezes the contents and night.

    The thermally controlled fan at least takes care of some of this by automatically increasing flow as the the ambient temperature lifts.

    I wrote an article for our local caravan mag on fridges, this involved recording temperatures. In December 2006 we spent 18 days in the Kruger Park. The remote sensor was on the bottom shelf of the fridge and the main sensor at the outside bottom vent to the fridge, in the tent area. The values for the period were;

    Min Ambient 9.2°C, Max 51.5°C.
    Max Fridge 13.0°, min -1.5°C

    That holiday we froze food 5 times due to the hysteresis of the fridge.

    Will look into PID.

    Why can one not have the ammonia permanently heated waiting for a top up to get it to boiling?

    I assume the cooling only takes place on boiling?

    The best performance of the fridge, in lower ambients, is on gas. This I put down to the fact that it is because the heating source is always present keeping the ammonia at temperature. I can't see a way to control the flame according to the ambient and internal temperature and therefore would like to emulate this using the element. It must be possible?

    Regards
    Andrew

Similar Threads

  1. Small domestic absorption fridge
    By Peter_1 in forum Domestic
    Replies: 30
    Last Post: 24-08-2011, 11:48 AM
  2. Kerosene flame heated absorption refrigerators
    By marvic in forum Technical Discussions
    Replies: 6
    Last Post: 27-08-2010, 03:21 AM
  3. Urgent: absorption chiller
    By nostalgia in forum Fundamentals
    Replies: 5
    Last Post: 11-08-2009, 09:59 PM
  4. Absorption chiller in winter
    By igorb73 in forum Technical Discussions
    Replies: 2
    Last Post: 16-03-2007, 08:09 AM
  5. Marine Wine Fridges
    By Globe76 in forum Trouble Shooting
    Replies: 33
    Last Post: 05-05-2006, 07:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •