    Daiken FLX60JVEA tries to start but cuts out



    like the title this daiken tries to start for a few seconds then it cuts out This is on heating mode every thing seems to worf ok for cooling mode ....any ideas



  2. #2
    PADDYC's Avatar
    PADDYC Guest

    Re: Daiken FLX60JVEA tries to start but cuts out

    I can see a green flashing light and after it cuts out there is also a sigle red light flashing and the green also

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daiken FLX60JVEA tries to start but cuts out

    Do you have a hard wired or hand held remote controller?
    Has a fault code been shown?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daiken FLX60JVEA tries to start but cuts out

    The FLX only comes with a hand held controller.

    You need to interrogate the unit to find the fault code. Search the forum for Daikin fault codes to find out how to interrogate the unit

    I suspect that the indoor coil sensor is at fault.

  5. #5
    PADDYC's Avatar
    PADDYC Guest

    Re: Daiken FLX60JVEA tries to start but cuts out

    Has fault L5 compressor motor ground/short circuit red yellow blue and brown all have a 1OHM restiance betweeen them is compressor stuffed?

  6. #6
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Daiken FLX60JVEA tries to start but cuts out

    megger test the compressor, if that's good then the inverter may be stuffed.
    I had a post in here a few times regarding daikins, and I remember being told, the compressor hardly ever stuffs up, but the inverter board fault is very common in the older ones.

    Can you test the inverter diodes with your multimeter? Their shouldn't be any diode test results below 0.4V, ie no shorts when testing one way, and testing the other way they should all be open circuit. If you don't know what I'm talking about, there's heaps of info on this site regarding testing inverter IPMs.
    I'm a fuji inverter tech though, not a daikin a/c tech.

    But without a megger test of the compressor, and a diode test of the IPM, you're only guessing at what is the cause of the fault.

    edit: VVVVV
    Temprite, you're the guy I got all my daikin advice from!
    Last edited by paul_h; 11-03-2009 at 02:28 PM.

  7. #7
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Daiken FLX60JVEA tries to start but cuts out

    Quote Originally Posted by paul_h View Post
    megger test the compressor, if that's good then the inverter may be stuffed.
    I had a post in here a few times regarding daikins, and I remember being told, the compressor hardly ever stuffs up, but the inverter board fault is very common in the older ones.
    Good advice. That fault,that model I would say 99.9% that the control PCB is dead.

  8. #8
    Join Date
    Dec 2008
    Location
    bucuresti
    Age
    47
    Posts
    16
    Rep Power
    0

    Re: Daiken FLX60JVEA tries to start but cuts out

    try to check diodeson IPM (inverter power module) L5 in the most causes has IMP defective

  9. #9
    Join Date
    Oct 2009
    Location
    ireland
    Age
    45
    Posts
    3
    Rep Power
    0

    Re: Daiken FLX60JVEA tries to start but cuts out

    test the in line fuse on the inverter board i had this problem recently compressor would start but once unit tried bringing on fan it would cause a fault and stop

  10. #10
    Join Date
    Aug 2008
    Location
    Worcestershire
    Age
    57
    Posts
    3
    Rep Power
    0

    Re: Daiken FLX60JVEA tries to start but cuts out

    Try doing a spin test on the outdoor fan. This can throw up an L5 fault i think as the fan motor is an inverter. Take the blade of and spin it by hand (motor must be unplugged) and it should spin 1-1/2 turns and not feel lumpy. Problem is the fan sometimes blows the PCB too.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Hard Start A Band Aid Fix ?
    By JoeKool in forum Fundamentals
    Replies: 1
    Last Post: 19-07-2008, 08:45 PM
  3. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Replies: 11
    Last Post: 02-03-2008, 06:10 PM
  4. 12V Fridge Won't Start
    By LeighC in forum Trouble Shooting
    Replies: 4
    Last Post: 07-12-2007, 03:26 PM
  5. Hard start, Soft Start, Inverter???
    By tkc100 in forum Fundamentals
    Replies: 9
    Last Post: 28-07-2007, 09:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •