    Current Overload Trip



    Hi all
    Have a problem occuring on site which read current overload we initialy thought the problem was due to power from the power generating company, but we tried it with generator power and the problem still arises. the setting on the UCM on the current overload settings the set configuration is 26 for 415 volts 50hz 3phase and compressor CHHN060 and running current on the compressor is 72Amps. any info will be helpfull. thanks



  2. #2
    mehen's Avatar
    mehen Guest

    Re: Current Overload Trip

    Are you working with inverters?
    If so, the overcurrent is due to refrigerant overcharge.
    best of luck...

  3. #3
    Join Date
    Aug 2009
    Location
    Mombasa
    Age
    57
    Posts
    27
    Rep Power
    0

    Re: Current Overload Trip

    No inverters being used the model of the unit is TRTAB 212

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Current Overload Trip

    Quote Originally Posted by Meer Abdulrehma View Post
    No inverters being used the model of the unit is TRTAB 212
    hi meer :
    current o.l couid be because of many reasons hi head pressure,, bad current transformers, bad contactor ,loose connection ,bad settings ,.
    u should check the unit when runnig ,i assume that after a serious inspection of these parameters u should be able to pinpoint your source of problem.
    good luck let us know how it went.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Current Overload Trip

    If overload is at 26amps and compressor is running at 72amps then I wouldn't blame the overload.

    What should eb correct/normal running current be?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Current Overload Trip

    If a six wire motor and overlaod monitoring one set of leads the overload should be set at half motor rated full load amps, ie 72amps FLA motor, o/load 26 amps.
    Check current draw with clip on ammeter.

  7. #7
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Current Overload Trip

    Quote Originally Posted by Brian_UK View Post
    If overload is at 26amps and compressor is running at 72amps then I wouldn't blame the overload.

    What should eb correct/normal running current be?
    this is a bad copy of the trane manual for setting ol on ucm controller 26 is a code not a current reading !!!!!
    as i said their must be another problem causingthis alarm
    §5 CURRENT OVERLOAD
    REFRIGERANT R22 - R404a
    COMPRESSOR
    CHHN 35 CHHN 40 CHHN 50 CHHN 60 ICHHB70 CHHB 85 CHHB 100
    RLA (A) 63 71 84 102 123 141 165
    380/50/3 CT ext. 10 10 01 01 02 02 03
    Dip switch 10011 11100 10011 11111 10001 11011 10010
    UCM confi 19 28 19 31 17 27 18
    RLA (A) 60 68 80 97 117 134 157
    400/50/3 CT ext. 10 10 01 01 02 02 03
    Dip switch 01111 11001 01111 11101 01101 11000 01110
    UCM confi 15 25 15 29 13 24 14
    RLA (A) 58 66 77 93 113 129 151
    415/50/3 CT ext. 10 10 01 01 02 02 03
    Dip switch 01101 10110 01100 11010 01011 10101 01011
    UCM confi 13 22 12 26 11 21 11
    RLA (A) 109 124 145 176 213 244 285
    220/50/3 CT ext. 02 02 02 03 04 04 05
    Dip switch 01000 10010 11101 10110 01101 11110 00111
    UCM confi 08 18 29 22 13 30 07


  8. #8
    Join Date
    Aug 2009
    Location
    Mombasa
    Age
    57
    Posts
    27
    Rep Power
    0

    Re: Current Overload Trip

    Hi Guys

    thanks for all your responses and concern have managed to solve the problem which ended up being the solenoid valves we have replaced and problem was solved.

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Scroll compressor current
    By Scott Buker in forum New Technologies
    Replies: 2
    Last Post: 02-10-2009, 11:54 PM
  3. Motor Current Fault York RecipPak YCUZ880E8
    By iaHVACguy in forum Trouble Shooting
    Replies: 0
    Last Post: 23-07-2009, 02:58 PM
  4. Replies: 14
    Last Post: 27-08-2008, 08:57 PM
  5. thermal Overload
    By marc5180 in forum Trouble Shooting
    Replies: 51
    Last Post: 03-11-2007, 10:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •