Thread: Natural air circulation
-
19-10-2009, 11:55 AM #1
Natural air circulation
Hi Guys,
A cold store sandwich panels manufacturer purpose on its manual the prevention of the freezing ground done by natural air circulation as it is show in the file.
I don't agree with this. Despite the the H value I don't see how it can achieve a less density value than at the inlet. I accept that if the tube at the outlet is heated around it (with electric heater bands for example).
If the air outlet tube is get colder inside than the inlet I even think that the air circulation should be at opposite sense.
What are your opinion about that? What your experience reveals?
Regards
To make progress is never good enough, I want to do better and better and better
-
19-10-2009, 06:40 PM #2
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: Natural air circulation
If holes are big and you use air force by fan that is ok. Or if the high of hole is more than 30 cm in dry area it is ok in wet area it should be more than 50 cm with air force
Last edited by mbc; 19-10-2009 at 06:42 PM.
-
20-10-2009, 01:56 AM #3
Re: Natural air circulation
I have seen these used in large storage facilities, but typically only in warmer climates.
If all else fails, ask for help.
-
20-10-2009, 05:09 AM #4
Re: Natural air circulation
HI Sadros
The method shown relies on the "Thermosysphon Effect" where a fluid in a tube is warmed in the upper region, this inturn expands and becomes lighter, with the differance of density flow occures. And you would be correct in assuming if the outlet were cooler than the inlet the air could flow in the opposite direction. But the differance in the head of pressure of the fluid incourages flow towards the outlet. The thermosyphon is used extensively on solar hot water systems.
-
20-10-2009, 11:04 AM #5
-
20-10-2009, 11:11 AM #6
Re: Natural air circulation
How the tube is warmed in the upper region? It would need to be more hot than at inlet so it could flow » (thermosyphon in solar hot water systems).
How the inlet can be more cold?!?
Now forgetting the effect of the tube heating, the hidrostatic force caused by the air column weight at the inlet and at outlet are the same, regardless the existing of tube or not. Don't you think?
RegardsTo make progress is never good enough, I want to do better and better and better
-
20-10-2009, 05:13 PM #7
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: Natural air circulation
The area you are going to put your cool rooms . ((Floor)) or the area has more moisture.
In my experience I use concrete block ( shape = H ) wide 25 cm/ High 30 cm/ length 40 cm
1-I lay those on floor
2- put 10 cm concrete on top of that
3- put 2 layer thick plastic sheet
4- put insulation (20 cm plastofom with P= 25kg )
5- put Min 10 cm concrete with metal bars
6 - I use forced air for crulation (air ventilation system)Last edited by mbc; 20-10-2009 at 05:31 PM.
Similar Threads
-
Natural Refrigerants
By baker in forum RefrigerantsReplies: 7Last Post: 26-10-2010, 05:28 PM -
Are there standard-systems for natural refrigerants?
By Moeller in forum RefrigerantsReplies: 9Last Post: 25-05-2009, 10:01 AM -
Ammonia Circulation rate - by Frick/ Vitler
By smpsmp45 in forum NH3Replies: 12Last Post: 16-06-2008, 10:06 AM -
natural Stratification tank
By Camille in forum IndustrialReplies: 0Last Post: 03-05-2007, 01:48 PM