    Natural air circulation



    Hi Guys,

    A cold store sandwich panels manufacturer purpose on its manual the prevention of the freezing ground done by natural air circulation as it is show in the file.

    I don't agree with this. Despite the the H value I don't see how it can achieve a less density value than at the inlet. I accept that if the tube at the outlet is heated around it (with electric heater bands for example).

    If the air outlet tube is get colder inside than the inlet I even think that the air circulation should be at opposite sense.

    What are your opinion about that? What your experience reveals?


    Regards
    Attached Files Attached Files


    To make progress is never good enough, I want to do better and better and better

  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Natural air circulation

    If holes are big and you use air force by fan that is ok. Or if the high of hole is more than 30 cm in dry area it is ok in wet area it should be more than 50 cm with air force
    Last edited by mbc; 19-10-2009 at 06:42 PM.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Natural air circulation

    I have seen these used in large storage facilities, but typically only in warmer climates.
    If all else fails, ask for help.


  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Natural air circulation

    HI Sadros
    The method shown relies on the "Thermosysphon Effect" where a fluid in a tube is warmed in the upper region, this inturn expands and becomes lighter, with the differance of density flow occures. And you would be correct in assuming if the outlet were cooler than the inlet the air could flow in the opposite direction. But the differance in the head of pressure of the fluid incourages flow towards the outlet. The thermosyphon is used extensively on solar hot water systems.

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Natural air circulation

    Quote Originally Posted by mbc View Post
    If holes are big and you use air force by fan that is ok. Or if the high of hole is more than 30 cm in dry area it is ok in wet area it should be more than 50 cm with air force
    Yes forced ventilation (fans) it's okay.

    What do you meant with dry and wet areas?

    Thanks.
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Natural air circulation

    Quote Originally Posted by Tesla View Post
    HI Sadros
    The method shown relies on the "Thermosysphon Effect" where a fluid in a tube is warmed in the upper region, this inturn expands and becomes lighter, with the differance of density flow occures. And you would be correct in assuming if the outlet were cooler than the inlet the air could flow in the opposite direction. But the differance in the head of pressure of the fluid incourages flow towards the outlet. The thermosyphon is used extensively on solar hot water systems.

    How the tube is warmed in the upper region? It would need to be more hot than at inlet so it could flow » (thermosyphon in solar hot water systems).
    How the inlet can be more cold?!?

    Now forgetting the effect of the tube heating, the hidrostatic force caused by the air column weight at the inlet and at outlet are the same, regardless the existing of tube or not. Don't you think?

    Regards
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Natural air circulation

    The area you are going to put your cool rooms . ((Floor)) or the area has more moisture.
    In my experience I use concrete block ( shape = H ) wide 25 cm/ High 30 cm/ length 40 cm
    1-I lay those on floor
    2- put 10 cm concrete on top of that
    3- put 2 layer thick plastic sheet
    4- put insulation (20 cm plastofom with P= 25kg )
    5- put Min 10 cm concrete with metal bars
    6 - I use forced air for crulation (air ventilation system)
    Last edited by mbc; 20-10-2009 at 05:31 PM.

Similar Threads

  1. Natural Refrigerants
    By baker in forum Refrigerants
    Replies: 7
    Last Post: 26-10-2010, 05:28 PM
  2. Are there standard-systems for natural refrigerants?
    By Moeller in forum Refrigerants
    Replies: 9
    Last Post: 25-05-2009, 10:01 AM
  3. Replies: 12
    Last Post: 16-06-2008, 10:06 AM
  4. natural Stratification tank
    By Camille in forum Industrial
    Replies: 0
    Last Post: 03-05-2007, 01:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •