Results 1 to 13 of 13
    eligray's Avatar
    eligray Guest
    Compressor too hot in chiller
    I've recently made a chiller with the following:
    ~6k BTU rotary "Rechi 39r131f"
    r507/404a TXV
    4x120mm 2000RPM fans on condenser
    SLHX
    propane as refrigerant
    Filter/drier
    Homemade receiver
    The problem I'm having is that my compressor gets extremely hot. Once the evaporator starts cooling off a bit, meaning that the restriction in the loop rises, the compressor gets quite quickly to very hot temps (80c+) I THINK that this is because there is far less oil flowing through the loop anymore, meaning that the compressor doesn't get the proper oil return. I have tried even putting a 250CFM leafblower-like fan on the compressor, and still it gets very hot, leading me to believe that there is not enough oil in the system. Oil may have escaped quite a bit when I did 10+ leak tests with propane when building my system.
    To have my system run safely, I've lowered the TXV restriction quite a bit, so that (in theory) it is getting more oil flow. The downside to this temporary fix is that my temps are very high (7c or so in the PC coolant loop)
    One time I left the system with the TXV turned to max restriction, with the 250 CFM fan on there. When I got back, the compressor was at 110c
    Would you guys confirm that too little oil is indeed my problem? Is there any way to just add some via a schrader valve?
    Thanks,
    Eli
    Apr 2001
    79
    5,071
    35
    Re: Compressor too hot in chiller
    It's not about the oil.
    Start here:
    http://www.refrigeration-engineer.co...ad.php?t=19701
    eligray's Avatar
    eligray Guest
    Any ideas of what it may be about, then?
    I didn't see anything in that thread that would relate to this issue here... but I am glad to know that gas can hurt a TXV
    11,025
    Quote Originally Posted by eligray View Post
    The you haven't absorbed the function of a suction cooled compressor yet.
    Oil lubricates, refrigerant cools.
    eligray's Avatar
    eligray Guest
    Also, I did notice quite a bit of oil escaping during repeated leak tests... I guess that may or may not be relevant.
    Split Croatia
    6,151
    That compressor is for dehumidifier/AC usage which mean high evaporation temperature. It is cooled with suction gases. If your system having low suction temperature and high suction superheat, than it will overheat.
    Question is what is saturated suction temperature and what is evaporator and total suction superheat?
    Apr 2001
    79
    5,071
    35
    Rotary compressors have the shell on the high side. They are supposed to run hot.
    Sep 2008
    427
    Hmmmm, I didn`t know that. Is that scroll compressors or just rotary ones as that could easily throw me next time I`ve problems on one.
    Thanks,
    Glenn
    Apr 2001
    79
    5,071
    35
    Quote Originally Posted by glenn1340 View Post
    Thanks,
    Glenn
    Just rotary compressors.
    You may have noticed that a rotary compressor always comes with an accumulator mounted on the inlet.
    The reason for this is that the suction gas goes directly to the compressor pump section. The pump discharges into the compressor shell, thus the shell is on the high side.
    eligray's Avatar
    eligray Guest
    Thank you very much for the info guys. I did realize that compressors would tend to have higher temperatures in a system like this than they would in a normal AC/Dehumidifier, but I didn't realize that they relied so heavily on suction gasses to stay cool.
    I'll measure data and post it in this thread next time I get a chance to run the system.
    Other than airflow, is there anything else that can be done to help cool the compressor? I'm sure it sounds stupid, but would a little extra oil help things out?
    I really appreciate your sharing the knowledge, thanks guys
    Feb 2009
    bruges
    42
    oil = lubrication of the inner parts
    One time I left the system with the TXV turned to max restriction, with the 250 CFM fan on there. When I got back, the compressor was at 110c One time I left the system with the TXV turned to max restriction, with the 250 CFM fan on there. When I got back, the compressor was at 110c
    that is because there is to little refrigerant in the evaporator witch gets you high sh.
    the task of a txv is measuring the SH.
    Jul 2010
    usa
    40
    your post is really good thanks for your post
    Sydneyman's Avatar
    Sydneyman Guest
    I have the super is too high, it can back to compressor about -2 to 5 degree C so general speaking it can cool down the compressor by system.
    I think you refrigerant have air inside, i suggest you to do to ways.
    1. open the condensor purge valve to get off the air.
    2. reclaim all refrigerant, and put the new refrigerant back to system, and have look the guage read..
    thanks
  1. process chiller help
    By talon771 in forum Industrial
    Last Post: 12-01-2011, 08:42 PM
  2. Absorption Chiller VS Mech. Chiller
    By Intern in forum Industrial
    Last Post: 30-05-2009, 08:31 AM
  3. York Chiller startup when on Emergency Power
    By Apollo10 in forum Trouble Shooting
    Last Post: 22-12-2008, 07:13 PM
  4. york chiller motor rotation error
    By cesarnino in forum Trouble Shooting
    Last Post: 13-12-2008, 03:43 PM
  5. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Last Post: 06-10-2008, 03:23 PM