    relative humidity



    just wondering
    when u are sizing up a evaportator, say for a cool room
    has 2300 watts load at 2 degrees, but needs to be at 75% RH, how do u work it out? so it does run at the correct RH?
    tx



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    894
    Rep Power
    19

    Re: relative humidity

    Hi there,

    There is no way to get the exact relative humidity you need, but you can get close. This depends to many factors first and the most important one is the evaporator TD (troom - tevaporation).

    Higher TD then lower RH.
    Lower TD then higher RH.

    Room wall and floor construction materials (outside layer), kind of product ,... directly affect RH in the room.

    Cheers
    Even Einstein Asked Questions

  3. #3
    patskE's Avatar
    patskE Guest

    Re: relative humidity

    how low/high of a td is say 50%? so i got a ball park figure :S

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: relative humidity

    Imagine your coldest point Te (evap) the air "could" be 100% RH (it has a certain fixed amount of actual water in it "weight") If this air is warmed to room temp with this fixed amount of water then the RH will drop. So colder the evap the lower the actual amount of water will exit.
    So answer to your question work out your actual water content at 2C and 75RH, then find out at what temperature this actual content reaches 100%, this then would be your Te temp.
    No allowance for entering moisture

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: relative humidity

    You need to use a LT chart, but can not spell "pyscrometric"

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: relative humidity

    Find 2'C at the bottom... follow this up to where it intersects with the 75%RH curve... then left to the 100%RH curve... then down. It ends up at -2'C. This is the coil surface temp/leaving air temp you need.

    In order to get -2'C surface temp, the evaporating temp of the refrigerant will need to be somewhat lower than -2'C.

    A 5'C TD coil should get you in the ballpark.
    Last edited by Gary; 18-10-2009 at 06:53 AM.

Similar Threads

  1. Relative humidity RH%
    By Carlo Hansen in forum Technical Speculations
    Replies: 40
    Last Post: 08-03-2010, 11:04 AM
  2. High humidity comfort cooling
    By Thermatech in forum Air Conditioning
    Replies: 70
    Last Post: 27-11-2008, 02:01 AM
  3. superheat
    By marco blanco in forum Trouble Shooting
    Replies: 48
    Last Post: 09-05-2007, 06:13 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. Relative Humidity Glycol Air Cooler
    By Friobernal in forum Fundamentals
    Replies: 4
    Last Post: 02-11-2003, 05:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •