    Exclamation High Stage Ultra Low Leak



    I'm working on a -86 degreee upright freezer. I have found a leak on the suction side of a Highstage compressor. Speaking with one of my coworkers i mentioned that i would like to replaced my cascade heat exchanger as with this brand I can not flush through my High Stage side of the heat exchanger ( no biggie there ) I also thought that replacing the compressor would be necessary because we probably pulled in moisture and ambient air into our system. This leak was found at the joint where the piping goes into the compressor. We are looking at a refrigeration system with AB oil ( similar to zerol 150) with a HPLC Grade Pentane as the oil sweeping agent and a charge made up of 70 percent R134a and 30 percent R410a.

    Again to me I tihnk this calls for an automatic compressor swap because there is no way to remove the oil and replace it with clean oil. The comrpessor comes pre charged with Oil from manufacturer, my co worker says look at the oil, if the oil looks good do not swap the compressor.

    I'm really asking for some opinions on this because I'm nervous about leaving in this compressor, even if the oil looks good.

    Any thoughts from any one on here??



  2. #2
    Join Date
    Dec 2008
    Location
    USA
    Age
    42
    Posts
    57
    Rep Power
    16

    Re: High Stage Ultra Low Leak

    No one can comment at all.. Waht the duece man!!!!!

  3. #3
    Join Date
    Dec 2008
    Location
    USA
    Age
    42
    Posts
    57
    Rep Power
    16

    Re: High Stage Ultra Low Leak

    Still nothing...

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: High Stage Ultra Low Leak

    Its on the high stage, then check the oil, if good, then nitrogen purge, deep vac (can repeat), then run, do not see the point in changing if all indications are OK, unless business is poor at the moment and you need the cash?

  5. #5
    Join Date
    Nov 2009
    Location
    united states
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: High Stage Ultra Low Leak

    it is recomended to replace the compressor by all ultra low manufactures.
    is it realy worth the risk of the unit failing a couple months down the road
    just when the customer places hundreds of thousands of dollars back in the unit.

  6. #6
    Join Date
    Dec 2008
    Location
    USA
    Age
    42
    Posts
    57
    Rep Power
    16

    Re: High Stage Ultra Low Leak

    dumbmechanic- I like your response.. It is correct! This was a while back when I posted and know how to approach this at this time.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. Ultra sonic leak detection
    By clivet in forum Tools and Calculators
    Replies: 18
    Last Post: 30-08-2010, 04:26 PM
  4. Two Stage Cooling
    By kev in forum Commercial
    Replies: 9
    Last Post: 15-05-2003, 11:55 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •