Results 1 to 2 of 2
    Co2_Scientist's Avatar
    Co2_Scientist Guest
    Danfoss WVFX Valve
    Okay so my boss has a system that uses a WVFX valve to control the water flow in the the heat exchanger. Recently this system has been shutting down the compressor on start up due the the high pressure overload switch. I think I have tracked this issue down the the before mentioned valve. The question I have is, have any of you had any experiences with rebuilding or repairing this kind of valve? I want to make sure the valve is operating as is should with out having to pay to get the system vac'ed down and filled back up. This is an older system filled with R-22, and last time we had a tech out for R-22 the cost was outrageous. So please any help or advice you can provide we with will be greatly appreciated.
    Thanks Robert
    11,025
    Re: Danfoss WVFX Valve
    Hi Robert,
    You can get service kits for that valve, details here...
    http://www.danfoss.com/NR/rdonlyres/.../PFD00A102.pdf
    Hopefully the refrigerant connections should be through a valved line or the capillary is via a Schraeder connector, so a reclaim and refill should not be required.
  1. ICS Danfoss valve
    By jax1 in forum NH3
    Last Post: 29-08-2010, 05:28 PM
  2. Danfoss water valve
    By glenn1340 in forum Industrial
    Last Post: 10-10-2009, 07:01 AM
  3. LEV does not open
    By Yuri B. in forum Air Conditioning
    Last Post: 19-07-2009, 02:37 PM
  4. Benji
  5. Danfoss PHTQ Valve
    By dallan in forum Industrial
    Last Post: 29-07-2006, 11:25 PM