    I have Daikin RXYQ12P7 and RXYQ10P7 with about 20 indoor units. Every indoor unit has accompanying BRC1D52 controller but none of them is "master" and earlier there was 2 master controllers for each VRV system. Additionally I have DSC601C51 Intelligent Touch controller.
    The problem is that I cannot change both systems from cool to heat mode.
    Any suggestions?



  2. #2
    Join Date
    Aug 2008
    Location
    england
    Age
    56
    Posts
    5
    Rep Power
    0

    Re: Daikin cool heat change

    check on the I controller that the mode function for all th areas in the building is not set to prohibited access if so change to permitted this will givr you the option to change the mode on the controllers from heat to cool

  3. #3
    AlPacino's Avatar
    AlPacino Guest

    Re: Daikin cool heat change

    It is not for sure. On the outdoor units, there are C/H selector option board, but there is no C/H selector switch attached to it. How can I disable C/H selector option and get the control via master BRC1D52 controller? I assume there is difference in setting the system with or without the C/H option board.

  4. #4
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: Daikin cool heat change

    Hi Alpacino.
    You have to check if the switch ds1-1 is on "off" position on the main outdoor board. ( cut the outdoor power supply if any change is done ).
    This setting disable the change over fonction by the A /B /C output.
    Then you can choose your master BRC, just press the change over button on the main selected BRC.
    Also you can fix it by setting the mode 22/ 9-01 to 9-02 on the BRC that will decide from cooling to heating...
    rgds
    cool#9

  5. #5
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin cool heat change

    Quote Originally Posted by cool#9 View Post
    Hi Alpacino.
    You have to check if the switch ds1-1 is on "off" position on the main outdoor board. ( cut the outdoor power supply if any change is done ).
    This setting disable the change over fonction by the A /B /C output.
    Then you can choose your master BRC, just press the change over button on the main selected BRC.
    Also you can fix it by setting the mode 22/ 9-01 to 9-02 on the BRC that will decide from cooling to heating...
    rgds
    cool#9

    cool#9,

    Can you explain more about code 22/9-01 and 9-02. What exactly does this set? Since it is a 22 code it is for an individual indoor unit. Does this define the master indoor unit for changeover control?

    Thanks.

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. System sizing for heat and manual J
    By Larry2 in forum Heat Pumps
    Replies: 5
    Last Post: 25-06-2008, 10:58 AM
  3. Heat Reclaim
    By chilled2005 in forum Supermarket Refrigeration
    Replies: 19
    Last Post: 05-05-2008, 05:32 PM
  4. Q=? h1=? mechanical schematics
    By fridg in forum Technical Speculations
    Replies: 22
    Last Post: 19-03-2006, 01:43 PM
  5. R134a <-> liquid heat exchanger design
    By DaBit in forum Technical Speculations
    Replies: 19
    Last Post: 10-05-2002, 08:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •