    carrier chiller aquasnap 30ra---160



    Circuit a, high pressure alarm fault unable to clear. circuit unable to start due to hp fault, unable to clear.Hp device not tripped, electrical circuit to device ok and unbroken. Pressure transducer ok. When hp fault is reset on control board within 30 seconds hp fault re-occurs. ...... im thinking a lap top is required here or new board. please advise.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: carrier chiller aquasnap 30ra---160

    Quote Originally Posted by mr saw View Post
    Circuit a, high pressure alarm fault unable to clear. circuit unable to start due to hp fault, unable to clear.Hp device not tripped, electrical circuit to device ok and unbroken. Pressure transducer ok. When hp fault is reset on control board within 30 seconds hp fault re-occurs. ...... im thinking a lap top is required here or new board. please advise.
    Hi Mr Saw.

    I am not sure of what age unit you have from the info supplied.
    Have a read of the attached.
    Hope it is of relavance?
    Check out the OAT Sensor if it is!
    Cheers Grizzly

  3. #3
    Join Date
    Apr 2003
    Location
    london
    Posts
    26
    Rep Power
    0

    Re: carrier chiller aquasnap 30ra---160

    not sure of age, will check today. i know it runs on r407c if this helps. going to run an outputs test and see what fails. cheers for your response.

  4. #4
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: carrier chiller aquasnap 30ra---160

    Excuse me if you have a dual HP switch & have already tried this;

    If those are like current Trane chillers with a dual HP switch, take the front cover off & push the small brass coloured reset switch on the upper front. Fools lots of people, that one!

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: carrier chiller aquasnap 30ra---160

    Quote Originally Posted by FreezerGeezer View Post
    Excuse me if you have a dual HP switch & have already tried this;

    If those are like current Trane chillers with a dual HP switch, take the front cover off & push the small brass coloured reset switch on the upper front. Fools lots of people, that one!

    Yet another good point!

    I have lost count the no of times I have stumbled around and then remembered that one!
    Grizzly

  6. #6
    Join Date
    Dec 2007
    Location
    u.k
    Posts
    12
    Rep Power
    0

    Re: carrier chiller aquasnap 30ra---160

    Have you checked the little blue reset button on the HP Switch. If this is ok then check you are getting an output from the pcb to the switch. On some of these models the HP switches a contactor next to the fan contactors.
    Hope this helps.

  7. #7
    Join Date
    Apr 2003
    Location
    london
    Posts
    26
    Rep Power
    0

    Re: carrier chiller aquasnap 30ra---160

    thanks for all the responses. sadly none solved the problem. also the chiller is dated 2007. please any more advise or is it time for the carrier engineer with this lap top.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  3. Carrier chiller catalouge
    By Bullet in forum Refrigeration Books
    Replies: 4
    Last Post: 05-10-2009, 03:21 PM
  4. Carrier Chiller Help
    By superswill in forum Trouble Shooting
    Replies: 7
    Last Post: 18-01-2007, 10:06 PM
  5. Carrier chiller oil migration
    By lowtech in forum Industrial
    Replies: 5
    Last Post: 30-04-2006, 04:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •