15-10-2009, 09:55 PM #1
carrier chiller aquasnap 30ra---160
Circuit a, high pressure alarm fault unable to clear. circuit unable to start due to hp fault, unable to clear.Hp device not tripped, electrical circuit to device ok and unbroken. Pressure transducer ok. When hp fault is reset on control board within 30 seconds hp fault re-occurs. ...... im thinking a lap top is required here or new board. please advise.
16-10-2009, 06:45 AM #2
16-10-2009, 07:05 AM #3
Re: carrier chiller aquasnap 30ra---160
not sure of age, will check today. i know it runs on r407c if this helps. going to run an outputs test and see what fails. cheers for your response.
16-10-2009, 10:11 AM #4
Excuse me if you have a dual HP switch & have already tried this;
If those are like current Trane chillers with a dual HP switch, take the front cover off & push the small brass coloured reset switch on the upper front. Fools lots of people, that one!
16-10-2009, 04:25 PM #5
16-10-2009, 05:17 PM #6
Have you checked the little blue reset button on the HP Switch. If this is ok then check you are getting an output from the pcb to the switch. On some of these models the HP switches a contactor next to the fan contactors.
Hope this helps.
17-10-2009, 11:29 AM #7
thanks for all the responses. sadly none solved the problem. also the chiller is dated 2007. please any more advise or is it time for the carrier engineer with this lap top.
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
Carrier chiller catalouge
By Bullet in forum Refrigeration BooksReplies: 4Last Post: 05-10-2009, 03:21 PM -
Carrier Chiller Help
By superswill in forum Trouble ShootingReplies: 7Last Post: 18-01-2007, 10:06 PM -
Carrier chiller oil migration
By lowtech in forum IndustrialReplies: 5Last Post: 30-04-2006, 04:11 PM