Thread: Samsung inverter a/c trouble
14-10-2009, 11:55 AM #1
Could anuone please help and tell me in samsung inverter air conditioner when you power the device all the lamps on front panel start blinking! I took the power cords out and let the device for 30 min to reset(?) but nothing! The problem remain. You give power and all start blinking! The problem occured when we had a power brake down but the unit was not working!!
14-10-2009, 05:51 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Samsung inverter a/c trouble
14-10-2009, 07:41 PM #3
Maube i should tell that it do not work from the front panel either. So you tell me that i go through the option codes in the remote controller and it will start up?
14-10-2009, 08:29 PM #4
follow the advise nike has given and will resolve the problem
Paul
"KEEP IT COOL"
16-10-2009, 08:00 AM #5
well open the compressor panel and note the error displayed on the PC board.
Refer to the installation manual & troubleshoot the unit!
16-10-2009, 05:15 PM #6
If i had an installation manual i would already done it...or the troubleshooting codes!! The problem was solved with nikes codes!!!! Thanks anuway...and special thanks to Nike!!
17-10-2009, 09:42 AM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Don't forget to add reputation!
SAMSUNG Inverter Errorcode E4
By samsunginverter in forum Air ConditioningReplies: 21Last Post: 05-08-2009, 11:28 AM