    Angry Daikin fault U4. relocated



    Been having such a ****ting time with Daikin floor console.
    1. fault U4
    2. got it going for a couple of days, then fault U4 occurs.
    3. Outdoor unit on temp/supply (flex lead plugged into power socket only).

    history: secondhand unit was working prior to disconnection.
    I had it degassed and regassed, then cleaned indoor unit washed filters and drum(s) installed at new location. Than all of the above happened.

    PLs help



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin fault U4. relocated

    A U4 fault indicates that the transmission signals between the indoor/outdoor unit PCB's is not happening.

    If, as you say, it worked fine before it was moved, then I would suggest that the transmission wiring has been installed incorrectly, i.e. the interconnect wire is the wrong specification, the interconnect cable has excess wires that are not earthed at 1 end, the interconnect wiring is adjacent to other cables causing interference, the transmission wire has been 'broken' through a local isolator etc.

    Without seeing the installation or knowing the age of the unit or the model number we are just guessing.

    My advice would be to run a temporary single wire connection between the indoor pcb and the outdoor pcb on the transmission terminal (No.2 on the old kit and No. 3 on the newer kit) and see if this solves the problem.
    Last edited by frank; 14-10-2009 at 09:04 PM.

  3. #3
    Matty whitelock's Avatar
    Matty whitelock Guest

    Re: Daikin fault U4. relocated

    Quote Originally Posted by frank View Post
    A U4 fault indicates that the transmission signals between the indoor/outdoor unit PCB's is not happening.

    If, as you say, it worked fine before it was moved, then I would suggest that the transmission wiring has been installed incorrectly, i.e. the interconnect wire is the wrong specification, the interconnect cable has excess wires that are not earthed at 1 end, the interconnect wiring is adjacent to other cables causing interference, the transmission wire has been 'broken' through a local isolator etc.

    Without seeing the installation or knowing the age of the unit or the model number we are just guessing.

    My advice would be to run a temporary single wire connection between the indoor pcb and the outdoor pcb on the transmission terminal (No.2 on the old kit and No. 3 on the newer kit) and see if this solves the problem.
    Thanks Frank, the outdoor unit model RXD60BVMA, indoor unit FLX60AVMA will try the above right after thread.

  4. #4
    Matty whitelock's Avatar
    Matty whitelock Guest

    Re: Daikin fault U4. relocated

    Wiring all correct with 230V between phase and neutral terminals on outdoor unit and interconnect and earth all connected correctly with no isolator. Interesting thing is this...unit works intermittantly (rather than not at all) on another power circuit with voltage of -7.94V on interconnect terminal. On the other circuit which doesn't work at all it shows exactly the same voltages but the indoor unit shows the blinking LED light instead of the solid. Likely cause electrical interference to the PCB? Even when the unit works it shows a blinking LED on the outdoor unit indicating to check the indoor unit. Will dedicate supply to narrow problem down. Are there any known issues with Diakin in relation to this?

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Daikin fault U4. relocated

    http://download407.mediafire.com/jxz...ocket+Book.pdf
    Hello Matty. I am not familiar with Daikin AC s but maybe the PDF through this link will be somehow helpful to you.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin fault U4. relocated

    Quote Originally Posted by Matty whitelock View Post
    Wiring all correct with 230V between phase and neutral terminals on outdoor unit and interconnect and earth all connected correctly with no isolator. Interesting thing is this...unit works intermittantly (rather than not at all) on another power circuit with voltage of -7.94V on interconnect terminal. On the other circuit which doesn't work at all it shows exactly the same voltages but the indoor unit shows the blinking LED light instead of the solid. Likely cause electrical interference to the PCB? Even when the unit works it shows a blinking LED on the outdoor unit indicating to check the indoor unit. Will dedicate supply to narrow problem down. Are there any known issues with Daikin in relation to this?
    The green LED on both the indoor and outdoor PCB's should be blinking under normal operation. The PCB LED blinks at a rate of 1/sec to indicate that the PCB is OK. The second green LED on the indoor PCB blinks/flashes in relation to the data transmission speed

Similar Threads

  1. Daikin VRV U4 FAULT
    By leegally1983 in forum Air Conditioning
    Replies: 14
    Last Post: 30-11-2010, 11:49 PM
  2. Daikin fault
    By SkyWalker in forum Air Conditioning
    Replies: 7
    Last Post: 16-09-2009, 09:09 PM
  3. Daikin r407c 2 pipe vrv ja fault code any offers?
    By Contactor in forum Air Conditioning
    Replies: 11
    Last Post: 28-07-2009, 01:26 AM
  4. Daikin Split f3 Fault
    By moondawn in forum Air Conditioning
    Replies: 18
    Last Post: 01-06-2009, 07:09 PM
  5. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •