14-10-2009, 09:33 AM #1
Daikin fault U4. relocated
Been having such a ****ting time with Daikin floor console.
1. fault U4
2. got it going for a couple of days, then fault U4 occurs.
3. Outdoor unit on temp/supply (flex lead plugged into power socket only).
history: secondhand unit was working prior to disconnection.
I had it degassed and regassed, then cleaned indoor unit washed filters and drum(s) installed at new location. Than all of the above happened.
PLs help
-
14-10-2009, 09:01 PM #2
Re: Daikin fault U4. relocated
A U4 fault indicates that the transmission signals between the indoor/outdoor unit PCB's is not happening.
If, as you say, it worked fine before it was moved, then I would suggest that the transmission wiring has been installed incorrectly, i.e. the interconnect wire is the wrong specification, the interconnect cable has excess wires that are not earthed at 1 end, the interconnect wiring is adjacent to other cables causing interference, the transmission wire has been 'broken' through a local isolator etc.
Without seeing the installation or knowing the age of the unit or the model number we are just guessing.
My advice would be to run a temporary single wire connection between the indoor pcb and the outdoor pcb on the transmission terminal (No.2 on the old kit and No. 3 on the newer kit) and see if this solves the problem.Last edited by frank; 14-10-2009 at 09:04 PM.
-
15-10-2009, 08:01 AM #3
-
15-10-2009, 08:19 AM #4
Re: Daikin fault U4. relocated
Wiring all correct with 230V between phase and neutral terminals on outdoor unit and interconnect and earth all connected correctly with no isolator. Interesting thing is this...unit works intermittantly (rather than not at all) on another power circuit with voltage of -7.94V on interconnect terminal. On the other circuit which doesn't work at all it shows exactly the same voltages but the indoor unit shows the blinking LED light instead of the solid. Likely cause electrical interference to the PCB? Even when the unit works it shows a blinking LED on the outdoor unit indicating to check the indoor unit. Will dedicate supply to narrow problem down. Are there any known issues with Diakin in relation to this?
-
16-10-2009, 03:43 PM #5
Re: Daikin fault U4. relocated
http://download407.mediafire.com/jxz...ocket+Book.pdf
Hello Matty. I am not familiar with Daikin AC s but maybe the PDF through this link will be somehow helpful to you.
-
16-10-2009, 09:20 PM #6
Re: Daikin fault U4. relocated
Similar Threads
-
Daikin VRV U4 FAULT
By leegally1983 in forum Air ConditioningReplies: 14Last Post: 30-11-2010, 11:49 PM -
Daikin fault
By SkyWalker in forum Air ConditioningReplies: 7Last Post: 16-09-2009, 09:09 PM -
Daikin r407c 2 pipe vrv ja fault code any offers?
By Contactor in forum Air ConditioningReplies: 11Last Post: 28-07-2009, 01:26 AM -
Daikin Split f3 Fault
By moondawn in forum Air ConditioningReplies: 18Last Post: 01-06-2009, 07:09 PM -
UA Daikin Fault Code
By jedi in forum Air ConditioningReplies: 2Last Post: 23-07-2007, 01:44 PM