    J have a problem with fujitsu in the trouble shooting say is 1flash and is communcation error -indoor - outdoor unt can you help me

    Problem E100 communication error indoor -outdoor unit
    Last edited by frank; 13-10-2009 at 07:17 PM.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fujitsu

    What is full model number?

  3. #3
    Join Date
    Jul 2008
    Location
    Australia
    Age
    76
    Posts
    21
    Rep Power
    0

    Re: Fujitsu

    At outdoor unit, disconnect the serial interconnecting cable (connects to a red wire inside unit) Use voltmeter to read between wire & Neutral. Should be 90 to 120 volts AC. If ok then try from neutral to terminal you took wire out of. Should be the same. If not ok on neutral to wire then indoor PCB not sending. If not ok between neutral & terminal then outdoor PCB not sending. NOTE there may be a faulty component damaging the PCB or blowing the DC fuse.

Similar Threads

  1. your opinons on fujitsu please
    By acgibo in forum Air Conditioning
    Replies: 18
    Last Post: 26-08-2009, 05:06 PM
  2. fujitsu wall mount volt free relay
    By mike live in forum Air Conditioning
    Replies: 3
    Last Post: 09-04-2009, 08:26 PM
  3. Fujitsu ducted error code
    By gille in forum Air Conditioning
    Replies: 9
    Last Post: 29-11-2008, 08:02 PM
  4. Fujitsu PCB
    By gwilliamson in forum Air Conditioning
    Replies: 6
    Last Post: 10-09-2008, 10:27 PM
  5. Fujitsu or not?
    By LRAC in forum Air Conditioning
    Replies: 14
    Last Post: 29-08-2007, 09:45 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •