    Copeland Compressor Suction Unloader



    What would be the accepted method of setting the two suction actuated unloaders on a copeland recip compressor. Running on R407C and they seem to be cutting in and out almost every second or two, so I think the differential is set too low. I wouldn't want to flood them back either (one of the compressors is getting an oil fault intermittently)This could be the electronic oil transducer, or too many starts, but most probably because the things keep cycling off without pumping down properly.

    Thanks


    a problem shared is a problem halved

  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,362
    Rep Power
    39

    Re: Copeland Compressor Suction Unloader

    I think you answered your own questions in a way .
    Depending on control system ( sounds like you have pressure switches ) but sometimes you can have timers to stop short cycling of unloaders .

    Compessor could also be not balanced for the load you have , if its never happy .

  3. #3
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Copeland Compressor Suction Unloader

    Quote Originally Posted by RANGER1 View Post
    I think you answered your own questions in a way .
    Depending on control system ( sounds like you have pressure switches ) but sometimes you can have timers to stop short cycling of unloaders .

    Compessor could also be not balanced for the load you have , if its never happy .
    Yes they have pressure switched, one for each unloader. On one of the compressors I thought I would widen the differential and get it running so it doesn't unload until it gets down to a reasonable level (just under 400) and then set it to load at 500 instead of 460 as it s now. Haven't thought about the back unloader yet.
    a problem shared is a problem halved

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Copeland Compressor Suction Unloader

    Try out frequency drive for compressor capacity control if the comp model has an oil pump .

Similar Threads

  1. Unloader
    By Abe in forum Fundamentals
    Replies: 6
    Last Post: 15-10-2009, 10:33 PM
  2. 5H86 Problems - Unloader Forks and Pins
    By 5H86User in forum Air Conditioning
    Replies: 13
    Last Post: 24-11-2008, 08:07 PM
  3. Can’t get a brine chiller down to temperature.
    By dkemper in forum Trouble Shooting
    Replies: 8
    Last Post: 08-06-2007, 03:38 PM
  4. carlyle 5H120 problems
    By old gas bottle in forum Industrial
    Replies: 4
    Last Post: 08-07-2006, 04:32 PM
  5. Unloader Set points
    By KeithCA in forum Trouble Shooting
    Replies: 4
    Last Post: 07-09-2005, 06:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •