    Need help Computer Room Air-con(CRAC) Problem



    Hi,
    I'm a facilities technician and working at the data center.Inside this data center,one of the rooms has 6 CRAC units and most of the units are sweating at compressor.Please advise Is it normal or something happened?

    Suction Pressure - around 60~68 psi
    Discharge Pressure-around 220~235 psi
    Scroll compressor

    I'm new in this site and sorry if my question is wrong.
    Thanks.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Need help Computer Room Air-con(CRAC) Problem

    Your question isn't wrong....just posted in the wrong section, but I've moved it now.

    Suction and discharge pressures mean nothing if you don't tell us what refrigerant it is? The air on and air off temperatures are also important.

    Also, the pressures should be converted to temperature to be of any use in determining if the system is operating correctly.

  3. #3
    Join Date
    Aug 2009
    Location
    Singapore
    Age
    47
    Posts
    42
    Rep Power
    0

    Re: Need help Computer Room Air-con(CRAC) Problem

    Thanks,Frank.
    Refrigerant is R-22 and air on and air off temperaturs are 17 and 21 deg F.

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Need help Computer Room Air-con(CRAC) Problem

    Hi there,

    Suction pressure seems OK. Discharge pressure with water cooled condenser is OK. Or with air cooled condenser with ambient temperature of around 30°C is OK.

    Measure super heat and sub cooling.

    If ambient humidity is high sweating is normal. If you have low super heat then there is a liquid flood back.

    Cheers
    Even Einstein Asked Questions

  5. #5
    Join Date
    Aug 2009
    Location
    Singapore
    Age
    47
    Posts
    42
    Rep Power
    0

    Re: Need help Computer Room Air-con(CRAC) Problem

    I'd like to know what ambient humidity is considered as high ambient humidity?

    Thanks.

  6. #6
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Need help Computer Room Air-con(CRAC) Problem

    above 50% rh but all dependes on temp!!! u should use a enthalpy table and that will tell u what your duepoint is!

  7. #7
    Join Date
    Aug 2009
    Location
    Singapore
    Age
    47
    Posts
    42
    Rep Power
    0
    Thanks a lot.
    Last edited by chillin out; 15-10-2009 at 09:47 PM.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need help Computer Room Air-con(CRAC) Problem

    Quote Originally Posted by ksm View Post
    ... air on and air off temperaturs are 17 and 21 deg F.
    That can't be right. Measure again.

    We are talking about the air temperature entering the evaporator coil and the air temperature leaving the evaporator coil, measured close to the coil.

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Need help Computer Room Air-con(CRAC) Problem

    ksm,
    hopefully you are talking air temps expressed in degrees C.
    Generally in data centres you need to keep the humidity level up by adding moisture with humidifiers, due to high sensible heat loads, get the humidity too low will create static problems in computers. And create the sweaty compressor problems you have.

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need help Computer Room Air-con(CRAC) Problem

    If the numbers are correct and indeed in degrees C, then the coil is running warmer than it should and the humidity is too high. Either unloading set too high or blower running too fast.

    But we really don't know if these systems have any form of unloading... and we don't know if the temperatures provided are accurate.

  11. #11
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Need help Computer Room Air-con(CRAC) Problem

    Reltive Humidity depends on the local ambient.If you are talking about Singapore it should be around 35 degree C and wet bulb temperature of 26 to 28 degree C and RH will be 50 to 80 %.
    When the suction of compressor has temperature(surface) less than dew point sweating will take place. And it is normal.
    From the way you have explainted it appears it is out door condensing unit and the ambient RH being high it must be sweating on the surface of suction side of compressor

  12. #12
    Join Date
    Aug 2009
    Location
    Singapore
    Age
    47
    Posts
    42
    Rep Power
    0

    Re: Need help Computer Room Air-con(CRAC) Problem

    Ok,thanks.Gary.
    I will check again.Thanks all.

Similar Threads

  1. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Replies: 5
    Last Post: 13-03-2009, 01:49 AM
  2. Help with Condensation in Fitness Room
    By S_Line in forum Trouble Shooting
    Replies: 37
    Last Post: 04-03-2009, 12:52 AM
  3. Inverters in server room
    By AbsoluteWDJ in forum Air Conditioning
    Replies: 35
    Last Post: 22-02-2009, 08:45 AM
  4. Computer Problem ?
    By Brian_UK in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 27-01-2009, 09:04 PM
  5. Computer Rooms
    By vspiteri in forum Industrial
    Replies: 20
    Last Post: 26-02-2002, 10:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •