Need help Computer Room Air-con(CRAC) Problem
Hi,
I'm a facilities technician and working at the data center.Inside this data center,one of the rooms has 6 CRAC units and most of the units are sweating at compressor.Please advise Is it normal or something happened?
Suction Pressure - around 60~68 psi
Discharge Pressure-around 220~235 psi
Scroll compressor
I'm new in this site and sorry if my question is wrong.
Thanks.
-
11-10-2009, 05:28 PM #2
Re: Need help Computer Room Air-con(CRAC) Problem
Your question isn't wrong....just posted in the wrong section, but I've moved it now.
Suction and discharge pressures mean nothing if you don't tell us what refrigerant it is? The air on and air off temperatures are also important.
Also, the pressures should be converted to temperature to be of any use in determining if the system is operating correctly.
-
11-10-2009, 05:42 PM #3
Re: Need help Computer Room Air-con(CRAC) Problem
Thanks,Frank.
Refrigerant is R-22 and air on and air off temperaturs are 17 and 21 deg F.
-
12-10-2009, 07:00 AM #4
Re: Need help Computer Room Air-con(CRAC) Problem
Hi there,
Suction pressure seems OK. Discharge pressure with water cooled condenser is OK. Or with air cooled condenser with ambient temperature of around 30°C is OK.
Measure super heat and sub cooling.
If ambient humidity is high sweating is normal. If you have low super heat then there is a liquid flood back.
CheersEven Einstein Asked Questions
-
15-10-2009, 04:49 PM #5
Re: Need help Computer Room Air-con(CRAC) Problem
I'd like to know what ambient humidity is considered as high ambient humidity?
Thanks.
-
15-10-2009, 05:35 PM #6
Re: Need help Computer Room Air-con(CRAC) Problem
above 50% rh but all dependes on temp!!! u should use a enthalpy table and that will tell u what your duepoint is!
-
15-10-2009, 05:42 PM #7
Thanks a lot.
Last edited by chillin out; 15-10-2009 at 09:47 PM.
-
15-10-2009, 06:26 PM #8
Re: Need help Computer Room Air-con(CRAC) Problem
-
16-10-2009, 02:09 AM #9
Re: Need help Computer Room Air-con(CRAC) Problem
ksm,
hopefully you are talking air temps expressed in degrees C.
Generally in data centres you need to keep the humidity level up by adding moisture with humidifiers, due to high sensible heat loads, get the humidity too low will create static problems in computers. And create the sweaty compressor problems you have.
-
16-10-2009, 03:11 AM #10
Re: Need help Computer Room Air-con(CRAC) Problem
If the numbers are correct and indeed in degrees C, then the coil is running warmer than it should and the humidity is too high. Either unloading set too high or blower running too fast.
But we really don't know if these systems have any form of unloading... and we don't know if the temperatures provided are accurate.
-
16-10-2009, 07:54 AM #11
Re: Need help Computer Room Air-con(CRAC) Problem
Reltive Humidity depends on the local ambient.If you are talking about Singapore it should be around 35 degree C and wet bulb temperature of 26 to 28 degree C and RH will be 50 to 80 %.
When the suction of compressor has temperature(surface) less than dew point sweating will take place. And it is normal.
From the way you have explainted it appears it is out door condensing unit and the ambient RH being high it must be sweating on the surface of suction side of compressor
-
16-10-2009, 01:22 PM #12
Re: Need help Computer Room Air-con(CRAC) Problem
Ok,thanks.Gary.
I will check again.Thanks all.
Similar Threads
-
Blind Cold room specs help
By frostedflake in forum Trouble ShootingReplies: 5Last Post: 13-03-2009, 01:49 AM -
Help with Condensation in Fitness Room
By S_Line in forum Trouble ShootingReplies: 37Last Post: 04-03-2009, 12:52 AM -
Inverters in server room
By AbsoluteWDJ in forum Air ConditioningReplies: 35Last Post: 22-02-2009, 08:45 AM -
Computer Problem ?
By Brian_UK in forum Chit Chat & Service StoriesReplies: 1Last Post: 27-01-2009, 09:04 PM -
Computer Rooms
By vspiteri in forum IndustrialReplies: 20Last Post: 26-02-2002, 10:51 PM