Results 1 to 11 of 11

Hybrid View

  1. #1
    Join Date
    Oct 2009
    Location
    UK
    Posts
    8
    Rep Power
    0

    Chiller questions

    I saw a component on the refrigerant pipework on a chiller and was told it was an Auto Air Vent, I dont know if thats right, also why would one be necessary if the circuit had been evacuated before gas charge?
    Also I think the circuit has a leak in the heat exchanger, what is the best way to be sure? putting a dye in the circuit to see if it goes into the water?

  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Chiller questions

    Auto air vent is on water pipes and not on refrigerant pipes.
    There is no way for valve to distinguish refrigerant gas from air. One who told you that is telling you rubbish, or I am lost something in translation.
    You probably saw something like this.
    Last edited by nike123; 11-10-2009 at 05:43 PM.

  3. #3
    Join Date
    Oct 2006
    Location
    CORDOBA -ARGENTINA
    Age
    75
    Posts
    69
    Rep Power
    18

    Re: Chiller questions

    Quote Originally Posted by nike123 View Post
    Auto air vent is on water pipes and not on refrigerant pipes.
    Far far away , there where centrifugal R11 chiller , working on Vacuum , so it have AUTO AIR VENT.

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: Chiller questions

    Quote Originally Posted by DEVITG View Post
    Far far away , there where centrifugal R11 chiller , working on Vacuum , so it have AUTO AIR VENT.
    not so far away and they are called purge units
    still used on r-123 units!!!

  5. #5
    Join Date
    Oct 2009
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Chiller questions

    Thanks for that

  6. #6
    Join Date
    Oct 2009
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Chiller questions

    What about knowing if a leak is in a heat exchanger?

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Chiller questions

    Quote Originally Posted by colsy View Post
    What about knowing if a leak is in a heat exchanger?
    Remove refrigerant, pressurizing system with nitrogen and see if pressure drops and pressure increase on evaporator.
    What gas is in it? If you have R22, you can take some water from the evaporator, boil it and put your leak detector (or halid torch) in the fumes. R22 dissolves in the water.
    What sort of heat exchanger do you have?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Oct 2009
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Chiller questions

    Thanks for that tip, I like the idea of boiling the water. The chiller is a Carrier with R407c gas, I was thinking to cut the pipework and pressure test the heat exchanger and the rest of the circuit seperately, but surely there are easier methods.

  9. #9
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Chiller questions

    maybe if you close al the automatic vents,or air-separators on the water circuit,and see if the pressure is rising.

    Ice

  10. #10
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Chiller questions

    What is the model number of your carrier chiller

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 09:42 PM
  2. Absorption Chiller VS Mech. Chiller
    By Intern in forum Industrial
    Replies: 20
    Last Post: 30-05-2009, 08:31 AM
  3. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning