    Danfoss water valve



    Hi everyone.
    I recently installed a water chiller to cool a solvent reclaimer, trouble is the machine was originally cooled on a total loss basis (costing my customer over £2000 p/a for water) so the condensor pressure was simply controlled by regulating in inlet water flow via a Danfoss WVFX valve.
    The situation now is that with the chiller and reclaim m/c running the Danfoss valve will be shut until the head pressure rises enough to open it. Until it opens the chiller pump will be pumping against a dead end.
    I`m going to install a bypass but I need to shut the bypass off as the head pressure rises to force the water through the condensor.
    Now here`s the question: Can I reverse the operation of the valve ie it closes on rising pressure? I seem to remember reading somewhere that it`s possible but I`m dammed it I can find it now.

    Many thanks guys



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Danfoss water valve

    As far as pump protection you only need a minimum flow, install a permenent small orifce (a piece of 1/4" tube) as a by-pass or if you want to go fancy a pressure relief valve, pretty standard in the heating game.

  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Danfoss water valve

    it should not take that much time to open valve .you have to pay more money if you pump is always on , put timer on your system fist your pump comes on then your system with minimum flow as same as mad told or put trottle valve parallel with Wvfx valve
    By putting this valve with timer and adjusting this valve you solve every thing even it give you time to operate you wvfx valve

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Danfoss water valve

    Quote Originally Posted by glenn1340 View Post
    Hi everyone.
    I recently installed a water chiller to cool a solvent reclaimer, trouble is the machine was originally cooled on a total loss basis (costing my customer over £2000 p/a for water) so the condensor pressure was simply controlled by regulating in inlet water flow via a Danfoss WVFX valve.
    The situation now is that with the chiller and reclaim m/c running the Danfoss valve will be shut until the head pressure rises enough to open it. Until it opens the chiller pump will be pumping against a dead end.
    I`m going to install a bypass but I need to shut the bypass off as the head pressure rises to force the water through the condensor.
    Now here`s the question: Can I reverse the operation of the valve ie it closes on rising pressure? I seem to remember reading somewhere that it`s possible but I`m dammed it I can find it now.

    Many thanks guys
    You simply install this valve in bypass and adjust minimum required flow for your pump.

  5. #5
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Danfoss water valve

    Cheers guys, a good couple of suggestions there.
    As always this is the place to come for answers.
    Now to my next question, anyone know what tomorrows winng lottery numbers will be

  6. #6
    Join Date
    Mar 2009
    Location
    ireland
    Posts
    87
    Rep Power
    16

    Re: Danfoss water valve

    might be off the wall here but i think that the wvfx valve should be mounted on the out let of the condensor ...this will mean that the condensor is allways full of water and by the time that takes to heat up your valve will be open.... might save you a lot of hassle also eliminating the chance of air in your water side

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Danfoss water valve

    Or this automatic bypass valve from Honeywell which can be bought through Plumb Center etc.

    http://content.honeywell.com/uk/home....1%20DU145.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Danfoss water valve

    Dear little
    no it should be in inlet water

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. LEV does not open
    By Yuri B. in forum Air Conditioning
    Replies: 7
    Last Post: 19-07-2009, 02:37 PM
  3. Danfoss PHTQ Valve
    By dallan in forum Industrial
    Replies: 5
    Last Post: 29-07-2006, 11:25 PM
  4. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •