Danfoss water valve
Hi everyone.
I recently installed a water chiller to cool a solvent reclaimer, trouble is the machine was originally cooled on a total loss basis (costing my customer over £2000 p/a for water) so the condensor pressure was simply controlled by regulating in inlet water flow via a Danfoss WVFX valve.
The situation now is that with the chiller and reclaim m/c running the Danfoss valve will be shut until the head pressure rises enough to open it. Until it opens the chiller pump will be pumping against a dead end.
I`m going to install a bypass but I need to shut the bypass off as the head pressure rises to force the water through the condensor.
Now here`s the question: Can I reverse the operation of the valve ie it closes on rising pressure? I seem to remember reading somewhere that it`s possible but I`m dammed it I can find it now.
Many thanks guys
-
08-10-2009, 10:15 PM #2
Re: Danfoss water valve
As far as pump protection you only need a minimum flow, install a permenent small orifce (a piece of 1/4" tube) as a by-pass or if you want to go fancy a pressure relief valve, pretty standard in the heating game.
-
09-10-2009, 08:46 AM #3
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: Danfoss water valve
it should not take that much time to open valve .you have to pay more money if you pump is always on , put timer on your system fist your pump comes on then your system with minimum flow as same as mad told or put trottle valve parallel with Wvfx valve
By putting this valve with timer and adjusting this valve you solve every thing even it give you time to operate you wvfx valve
-
09-10-2009, 10:07 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Danfoss water valve
You simply install this valve in bypass and adjust minimum required flow for your pump.
-
09-10-2009, 01:42 PM #5
Re: Danfoss water valve
Cheers guys, a good couple of suggestions there.
As always this is the place to come for answers.
Now to my next question, anyone know what tomorrows winng lottery numbers will be
-
09-10-2009, 03:30 PM #6
Re: Danfoss water valve
might be off the wall here but i think that the wvfx valve should be mounted on the out let of the condensor ...this will mean that the condensor is allways full of water and by the time that takes to heat up your valve will be open.... might save you a lot of hassle also eliminating the chance of air in your water side
-
09-10-2009, 07:23 PM #7
Re: Danfoss water valve
Or this automatic bypass valve from Honeywell which can be bought through Plumb Center etc.
http://content.honeywell.com/uk/home....1%20DU145.pdfBrian - Newton Abbot, Devon, UK
Retired March 2015
-
10-10-2009, 07:01 AM #8
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: Danfoss water valve
Dear little
no it should be in inlet water
Similar Threads
-
Hoshizaki Ice Maker
By Abe in forum Legal-Business-MarketingReplies: 19Last Post: 01-05-2010, 03:27 AM -
LEV does not open
By Yuri B. in forum Air ConditioningReplies: 7Last Post: 19-07-2009, 02:37 PM -
Danfoss PHTQ Valve
By dallan in forum IndustrialReplies: 5Last Post: 29-07-2006, 11:25 PM -
open cycle R718 A/C that also provides high purity water?
By star882 in forum Technical SpeculationsReplies: 7Last Post: 27-07-2006, 04:18 AM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM