    Compressor Limts / Envelope

    hi all

    I am trying to understand what causes the compressor limits / envelope , or to be more precise the maximum evaporating temperature SST given by the manufacturer.
    In that is it the temperature of the return gas that would give insufficent cooling to the suction cooled windings or is it the pressure relevant to the SST that would overload the compressor due to a high suction pressure ?

    If anyone could help me it would be great;y appreciated

    Thanks

  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Compressor Limts / Envelope

    Limits,
    Understanding the compressor first.
    If it is a fixed speed, the it can move a certain volume. How dense the inlet refrigerant you are moving and how far you are moving it determines how much power you require(suction to discharge) "Like driving a car up a hill."
    Then you need to know the efficiency of the compressor, both mechanically and electrically (for semi and hermetic)
    This gives you your upper limit.
    When you have low(er) suction pressure, (you have less refrigerant mass) you increase your compression ratio, which increase the discharge temperature (which if it gets to hot can cause problems with oil and some parts of the machinery), If in some cases the motor inside the compressor is gas cooled (often known as suction cooled compressor) then a certain amount of mass of refrigerant is required to remove the heat from the motor. The refrigerant internally becomes greatly superheated.
    These combinations determine the lower limits.
    You also have limits on minimum compression ratios, valves can chatter if ratios are to low
    Plus the manufactures are sometimes a little conservative especially around maximum SST.
    Hope this is enough

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Post Re: Compressor Limts / Envelope

    Quote Originally Posted by mad fridgie View Post
    Limits,
    Understanding the compressor first.
    If it is a fixed speed, the it can move a certain volume. How dense the inlet refrigerant you are moving and how far you are moving it determines how much power you require(suction to discharge) "Like driving a car up a hill."
    Then you need to know the efficiency of the compressor, both mechanically and electrically (for semi and hermetic)
    This gives you your upper limit.
    When you have low(er) suction pressure, (you have less refrigerant mass) you increase your compression ratio, which increase the discharge temperature (which if it gets to hot can cause problems with oil and some parts of the machinery), If in some cases the motor inside the compressor is gas cooled (often known as suction cooled compressor) then a certain amount of mass of refrigerant is required to remove the heat from the motor. The refrigerant internally becomes greatly superheated.
    These combinations determine the lower limits.
    You also have limits on minimum compression ratios, valves can chatter if ratios are to low
    Plus the manufactures are sometimes a little conservative especially around maximum SST.
    Hope this is enough
    Exactly so. I especially like the car-up-the-hill analogy.

    Can this motor drive the car up the hill without overloading?

    That depends:

    a. How heavy is the car (mass refrigerant flow)?

    and

    b. How steep is the hill (compression ratio)?

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Compressor Limts / Envelope

    Quote Originally Posted by Gary View Post
    Exactly so. I especially like the car-up-the-hill analogy.

    Can this motor drive the car up the hill without overloading?

    That depends:

    a. How heavy is the car (mass refrigerant flow)?

    and

    b. How steep is the hill (compression ratio)?
    Cheers Gary, I think that explains it very well

  5. #5
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: Compressor Limts / Envelope

    Thanks Guys
    that helps me
    great analogy Gary!

    So I guess I am trying to say if i can keep the suction pressure down with a CPR that will stop the compressor overloading , but i think the return gas could be above the maximun SST given as the evaporatoe pressure temp could be high . ?

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Compressor Limts / Envelope

    Quote Originally Posted by kfjoe View Post
    Thanks Guys
    that helps me
    great analogy Gary!

    So I guess I am trying to say if i can keep the suction pressure down with a CPR that will stop the compressor overloading , but i think the return gas could be above the maximun SST given as the evaporatoe pressure temp could be high . ?
    May be your are confusing SST (saturated suction pressure, or in other words a temperature and pressure at which both liquid and vapour exist with no further changes happening like in a closed refrigerant bottle) and superheat. You have a maximum SST (maximum weight of the car) and controllerd by the CPR and maximum superheat (the difference between the SST and the actual temperature) if the superheat is to high, then discharge temp can be to high.
    The CPR should not be used as a main control but for short term protection (after defrost, or short bursts of high load)
    How the superheat is affected by the CPR is dependent on the system. (this is where you will get different points of view) A CPR causes a pressure drop thus in therory increase superheat, but A CPR resticts the flow out of the evaporator thus allowing the evap to have more liquid in than normal, possibly causing a slight wet suction, so when this wet suction goes through the CPR at little bit of phase change can happen and no excessive superheat occurs (a bit hard to write in a few words)

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor Limts / Envelope

    Quote Originally Posted by kfjoe View Post
    Thanks Guys
    that helps me
    great analogy Gary!

    So I guess I am trying to say if i can keep the suction pressure down with a CPR that will stop the compressor overloading , but i think the return gas could be above the maximun SST given as the evaporatoe pressure temp could be high . ?
    This is an area where mad fridgie and I have a technical disagreement.

    I say that the CPR, (installed near the compressor inlet) will do the trick no matter what the evap pressure/temp does.

    Try it out and let us know if the discharge temp rises.

  8. #8
    Join Date
    Sep 2009
    Location
    China
    Posts
    11
    Rep Power
    0

    Re: Compressor Limts / Envelope

    Quote Originally Posted by mad fridgie View Post
    Limits,

    When you have low(er) suction pressure, (you have less refrigerant mass) you increase your compression ratio, which increase the discharge temperature (which if it gets to hot can cause problems with oil and some parts of the machinery), If in some cases the motor inside the compressor is gas cooled (often known as suction cooled compressor) then a certain amount of mass of refrigerant is required to remove the heat from the motor. The refrigerant internally becomes greatly superheated.
    The internal compression ratio is constant due to constant internal volume ratio for Piston/Srew/Scroll compressors. Evap Temp(ET), Cond Temp (CT) and presssure drop of suction line and discharge line will also affect the compressor operation.

    ET -pressure drop of suction line , decide SST, which plus SH will decide the compressor inlet condition, including mass flow.

    and then, internal pressure of compressors can be gotten due to fixed compressor ( constant internal volume ratio), discharge pressure, is NOT equal to the internal pressure of compressors, and affect by the pressure drop and actual condensing pressure which is up to the heat exchanger performance.

    So DST maybe increase , or also Not.

    I agree that low mass flow will affect the compressor's low limit.

  9. #9
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Compressor Limts / Envelope

    Quote Originally Posted by Joey.zhang View Post
    The internal compression ratio is constant due to constant internal volume ratio for Piston/Srew/Scroll compressors. Evap Temp(ET), Cond Temp (CT) and presssure drop of suction line and discharge line will also affect the compressor operation.

    ET -pressure drop of suction line , decide SST, which plus SH will decide the compressor inlet condition, including mass flow.

    and then, internal pressure of compressors can be gotten due to fixed compressor ( constant internal volume ratio), discharge pressure, is NOT equal to the internal pressure of compressors, and affect by the pressure drop and actual condensing pressure which is up to the heat exchanger performance.

    So DST maybe increase , or also Not.

    I agree that low mass flow will affect the compressor's low limit.
    Thanks Joey, I think what Joey is saying, is that if you had you discharge pipe (outlet) is open (no restrictions) then changing your inlet pressure/mass flow will not change the internal compression ratio, because we have a fixed swept volume. How ever in practice the discharge is not open it is restricted (condensor & TEV) then changes to the inlet to the compressor change compression ratios, because the outlet remains more constant in comparission.

  10. #10
    Join Date
    Sep 2009
    Location
    China
    Posts
    11
    Rep Power
    0

    Smile Re: Compressor Limts / Envelope

    Quote Originally Posted by mad fridgie View Post
    Thanks Joey, I think what Joey is saying, is that if you had you discharge pipe (outlet) is open (no restrictions) then changing your inlet pressure/mass flow will not change the internal compression ratio, because we have a fixed swept volume. How ever in practice the discharge is not open it is restricted (condensor & TEV) then changes to the inlet to the compressor change compression ratios, because the outlet remains more constant in comparission.
    Thank Mad for the explanation. Yes, you are correct. Compression ratio will change in pratice as SST and SH varies. Compression ratio may either incease or decrease if the SST is lower, because compressor will over or off compress in pratice due to effect of the actual condensing compressor.

  11. #11
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Compressor Limts / Envelope

    kfjoe, confused yet?
    A very good question, very hard to explain in a few words

  12. #12
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Compressor Limts / Envelope

    Piston compressors are NOT fixed Vi machines providing the valves are pressure activated....If they seated and unseated by mechanical means the compressor makes a Vi; which may be near or far from the system's operating requirements.

    High suction pressures make high inlet side velocities and high top of piston pressures. The high velocities largely effect suction filters and similar but can lead to oil lift....The high pressures lead to both high motor loads and high stresses on pistons, rods, crank and so on.

  13. #13
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Compressor Limts / Envelope

    Hi Iso, I aplogise if I insulted you, but you did change the working conditions. This does make me a little suspicious?
    DesA clearly states my (our) reasons for being cautious.
    Like many on here, we are willing to assist if we can (for the good of the industry), but we are not here to give away our Intelectual Property!
    Pay the cash , then not a problem!
    $$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor Limts / Envelope

    Where there is giving without taking there is no incentive.

    Where there is taking without giving there is no justice.

    Where there is give and take in both directions there is balance and everyone benefits.

    What goes around should come around.
    Last edited by Gary; 30-10-2009 at 03:05 PM.

  15. #15
    Join Date
    May 2009
    Location
    china
    Posts
    18
    Rep Power
    0

    Re: Compressor Limts / Envelope

    Quote Originally Posted by Gary View Post
    Where there is giving without taking there is no incentive.

    Where there is taking without giving there is no justice.

    Where there is give and take in both directions there is balance and everyone benefits.

    What goes around should come around.

    Agree!
    That makes the forum more reasonable

  16. #16
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Compressor Limts / Envelope

    ^ A sage in our midst... indeed. Excellent.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  17. #17
    Join Date
    Oct 2006
    Location
    london
    Age
    47
    Posts
    13
    Rep Power
    0

    Re: Compressor Limts / Envelope

    few....!
    and relax!