    Industrial Chiller



    I need help with this requirement in Kenya

    Product: Cooking Oil
    Temperature 65 Celcius
    Located in Holding Tank
    Quantity 5 Tonnes in weight


    Cooling requirement
    To cool product down to 5 Celcius


    What chiller will I require?


    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Industrial Chiller

    (65 -5) x 5000 x 0,4 x 1.16 = 174.000 W or 174 kW if you want to it in 1 hour. This is pure theoretically, so I should add something for losses. So take 200 kW.
    Or +/- 20 kW for a 10 hours cooldown Abe. Will be then a +/- 10 HP.
    Last edited by Peter_1; 09-10-2009 at 09:05 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26

    Re: Industrial Chiller

    Thx Peter

    Greatly appreciated
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Industrial Chiller

    Consider a double section plate heat exchanger and the first stage use water and a cooling tower to drop oil temp to wet buld range and then second part of HX use chilled water down to design, this will reduce power consumption and require a smaller chiller.
    magoo

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Industrial Chiller

    Quote Originally Posted by Magoo View Post
    Consider a double section plate heat exchanger and the first stage use water and a cooling tower to drop oil temp to wet buld range and then second part of HX use chilled water down to design, this will reduce power consumption and require a smaller chiller.
    magoo
    I totally agree with you Magoo.
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Industrial Chiller

    Hi again Abe,
    if the cooking oil is exposed to food product, then it is quite likely to be saturated with crumb and the like, so make sure you include very good filtration and parallel filtering systems to protect HX from blockages.
    Alfa Laval do alot of similar applications with dairy industry, but with out the sediment content.
    WTT is another supplier, part of the GEA conglomeret bunch of companies.
    With first stage water cooling, you could think of specifying a closed circuit/ dry cooler type circuit to reduce any cross contamination with plate seal failure potential. The restackable/ serviceable dual circuit HX's would be preferable.

    magoo

  7. #7
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Industrial Chiller

    Because this is only a small holding tank I would suggest, it is manufactured with dimple plates, and an agitator. very simple and fool proof.
    depending upon your daily load profile and how it is batched, you can determine how many dimple plates circuit you require.
    Example One set water, One set refrigerant,
    Or one set water, second water from ice builder

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 09:42 PM
  2. Absorption Chiller VS Mech. Chiller
    By Intern in forum Industrial
    Replies: 20
    Last Post: 30-05-2009, 08:31 AM
  3. York Chiller startup when on Emergency Power
    By Apollo10 in forum Trouble Shooting
    Replies: 3
    Last Post: 22-12-2008, 08:13 PM
  4. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  5. Industrial water chiller
    By ibraheem in forum Fundamentals
    Replies: 4
    Last Post: 07-06-2008, 12:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •