07-10-2009, 02:31 PM #1
New Freezer Room, what do you recommend?
Hi all, have a job coming up installing a new freezer plant. Room size is 8.7 metres wide, 6.0 metres long and 8.1 metres high (internal measurements). Freezer is to store seafood, mainly prawns and will need to run around -30 degrees celsius in a maximum 38 degree ambient temp. when being loaded with prawns going in at approx -20 there will be anywhere upto 20 ton according to customer. Im looking at a copeland 45 hp compressor with remote condenser which will give me about 28kw @ - 35 sst. As far as energy efficiency / running costs has anyone got some advice or recommendations, it would be good to get your input.
regards
Beachbum
07-10-2009, 04:43 PM #2
Re: New Freezer Room, what do you recommend?
i suppose the obvious one is use a pack or inverter comp set up so it has not one big unit thumping away ,or i would have two systems with some spare capacity incase of a failure and also set so it could cycle on one when not under load.buts thats just my way.
07-10-2009, 05:51 PM #3
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
What is your compressor Type?
is it one stage or two stage compressor?
-35 SST I think it is better you use two stage compressor
08-10-2009, 05:09 AM #4
im with the old gas bottle,probably two comp rack with unloaders,id steer away from the copeland as i found on another thread id started (warning)it appears they are made to shift oil,well that was my interpretation of it anyway.run with bitzer with condensing at 43 deg.C. for allowance over the coming years as things dont seem to be cooling down to much,fan speed controller also.
08-10-2009, 09:18 AM #5
I think the customers logic of bringing down the temp in the cold store is not right. Typically the material shall be under packed conditions / may be pallets. The heat transfer through that is a very difficult task. unless he is keeping them in cartons itself. So selecting the unit for -30 deg is not the right solution.
Maneurop MT51HK4A - Freezer Room
By Hatchy in forum Trouble ShootingReplies: 35Last Post: 09-08-2010, 12:10 PM -
Cold room/ Freezer combo.
By dogma in forum CommercialReplies: 14Last Post: 09-11-2008, 02:25 PM -
Freezer Room Defrost
By Samarjit Sen in forum CommissioningReplies: 23Last Post: 21-06-2007, 06:16 AM -
Misa Kit Freezer Room
By Abe in forum CommercialReplies: 2Last Post: 03-01-2007, 09:04 PM -
Freezer Room Panels
By Feeze in forum Technical DiscussionsReplies: 10Last Post: 22-04-2005, 05:58 AM