    Jul 2008
    Singapore
    37
    15
    Question Total Heat Rejection
    Someone can help/guide me how to calculate the heat rejection for Air-cooled chiller.
    11,024
    Re: Total Heat Rejection
    Umm, cooling load plus motor power if in circuit.
    Oct 2001
    Nottingham UK
    5,667
    The heat rejected at the condenser will be equal to the heat absorbed at the evaporator plus the heat of compression, if the system is in balance.
    So, to answer your question, you must first calculate the heat absorbed (cooling load) and then add the heat of compression.