    Question Total Heat Rejection



    Someone can help/guide me how to calculate the heat rejection for Air-cooled chiller.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Total Heat Rejection

    Umm, cooling load plus motor power if in circuit.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Total Heat Rejection

    The heat rejected at the condenser will be equal to the heat absorbed at the evaporator plus the heat of compression, if the system is in balance.

    So, to answer your question, you must first calculate the heat absorbed (cooling load) and then add the heat of compression.