    Celler Cooling A/C or Refrigeration



    Hi Guys,

    When does a/c become refrigeration and vice versa
    Why do i ask

    Today i got called to a celler cooler in Norwich which turned out to have a seized compressor

    The condensing unit is a Eaton Williams, J 97643-02 S/N Q08591 2003

    Now the compressor is a L'unite Hermatec RK5515C R407c 240v which according to the NRS book is an a/c pot

    Now the system is much like an a/c system, boxed indoor and outdoor unit. all that has to be done is pipe and wire between them. No drier.

    Which brings me to another question, why do a/c units never have driers on them. Bi-Directional one's readily available from all stockists.

    I have asked the office to quote for a pot, liquid & Suction driers as the unit is cool only and the reclaim and use fresh gas.

    So many questions, too slow typing speed

    Regards

    Fatboy
    Last edited by Latte; 28-10-2004 at 07:58 PM. Reason: spelling - fingers too fat fot keys



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Celler Cooling A/C or Refrigeration

    A lot of packaged a/c condensing units already have driers built into them - they're not big but are there - more like a cap line drier size.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Celler Cooling A/C or Refrigeration

    Hi Marc,

    Remember, it is me you are talking to

    Quote Originally Posted by Marc O'Brien
    AC compressor viscosities of 62 centistokes is fine for saturated evaporating temps around the 0°C mark.

    Warmer refrigerant temperatures tollerate higher moisture PPM's.

    Can you translate this from technical director level to basic engineers level

    Thanks

    Ray

  4. #4
    rbartlett's Avatar
    rbartlett Guest

    Re: Celler Cooling A/C or Refrigeration

    eaton williams bought the remains of qualitair (my first employer)

    their cellar cooler (used to be QKK -err 'qualitair keller kooler')
    was basically an air conditioning condenser with a different (noisy) evaparator..

    anyway all a/c's have a drier but it's a tiny copper spun one..

    I remember when the japanese first came over and we used to see loads with a drier -plus a sightglass- fitted in the expansion line

    cheers

    richard

  5. #5
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Celler Cooling A/C or Refrigeration

    Hi Guys,

    Thanks for the replies, so what is the consensous of opinion on the drier front.

    I am tempted to fit one with a sightglass on the liquid line, anyone disagree with this

    Regards

    Raymond

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Celler Cooling A/C or Refrigeration

    Which brings me to another question, why do a/c units never have driers on them.
    On most (recent) A/C units the expansion device is on the outdoor unit to save space on the indoor unit and the liquid line between the outdoor shutoff valve and the indoor unit is part of the evaporator. Therefore it should not have a drier or sight glass installed in it. This is another reason why you will see both the liquid and suction lines insulated on air conditioning split systems.

    Does your outdoor unit have an EEV or capillary? If not then you can safely fit both a drier and sight glass. A sight glass fitted after the metering device is just a waste of £'s.

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Celler Cooling A/C or Refrigeration

    Hi Raymond.

    In the manufacturer catalogue, you will see for each compressor model, the minimum evaporating temp. This one can go as low as -10C (evap. temp.)

    It is not important if you call it refrigeration or AC, its the working conditions that count.

    According to the manufacturer, this is an AC compressor and its the firs time I've heard that it is used for refrigeration.
    AJ 5515C or AJ5518C will do a better job depending on your evap. temp.

    Chemi

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Celler Cooling A/C or Refrigeration

    Quote Originally Posted by rdocwra
    I am tempted to fit one with a sightglass on the liquid line, anyone disagree with this
    I don't know this unit but it all depends on where the expansion device is. If it is at the evaporator then by all means go ahead with your plan - if it is at the condensing unit then your sight glass will never be full and some idiot, at a later date, may try and charge to a flooded sight glass
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Celler Cooling A/C or Refrigeration

    Hi Guys,

    I cannot remember see a metering device on the outdoor unit.

    I will get a drier and sightglass just in case and will also check the evap just to make sure there is either cap tube or an expandion valve inside.

    regards

    Fatboy

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Celler Cooling A/C or Refrigeration

    Hi Raymond,

    I do not believe that a manufacturer will not put as a standard equipment, a drier and sight glass.

    What I do believe, is that the person who installed it at the first place, didn't.

    If there is a cap tube, you will see the drier just before it.

    In AC splits, there is no drier and many people, by mistake, think that what they see before the cap tube is a small drier. It is not. What it is, is a very fine filter to keep the cup tube clean.

    Chemi

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Celler Cooling A/C or Refrigeration

    Not quite true Chemi. See this link http://www.spincometal.com/mp_driers.htm

  12. #12
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Celler Cooling A/C or Refrigeration

    Thanks Frank.

    I have learnt something today.
    The local manufacturers do not use them.
    I have this practice that when a cap tub is blocked, the first thing I check is that filter. Never saw anything else but the fine mash inside.

    Every day you learn something new!

    Chemi

    P.S. Isn't it CELLAR?

  13. #13
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Celler Cooling A/C or Refrigeration

    Marc

    Next time God is dishing out the brains............please dont be selfish, leave a little for " us" as well !!!!
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Celler Cooling A/C or Refrigeration

    Quote Originally Posted by Marc O'Brien
    Not quite true, Chemi. I am one of those who was born knowing all, forgetting a little bit more every day.
    Then we're two.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Dec 2001
    Location
    Norway
    Posts
    13
    Rep Power
    0

    Thumbs up Re: Celler Cooling A/C or Refrigeration

    Hey folks,interesting discussion ,if you have a cap tube and
    and increase volume after the condenser you will move the
    balance point for the amount of refrigerant you should put
    there,its important to have the right condition to inlet of the
    cap tube,because of the two-phase flow calculated by the
    factory.If this is an old secondhand compressor you better
    check for acids by oiltesting and choose a small laying filter
    which take care of acid/water.I dont try to learn you something you know, I am only interested in subjects like this.
    Have nice day! norcool
    norcool

  16. #16
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Celler Cooling A/C or Refrigeration

    when God was giving out brains, i thought he said "trains" and i said "give me a slow one, that goes chug chug."

    cheers


    eggs

  17. #17
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Celler Cooling A/C or Refrigeration

    you got it, tiger.

  18. #18
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Celler Cooling A/C or Refrigeration

    Quote Originally Posted by Peter_1
    Then we're two.
    Listening to you two reminds me of the old poem:-

    There's none so queer as folk dear
    except thee and me,
    But you're a little bit funny yourself.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  19. #19
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Celler Cooling A/C or Refrigeration

    i'd watch it if i were you, cos i know a poem aswell.
    Roses are red
    Violets are blue
    i used to be schizophrenic
    so did i.

    cheers

    eggs

  20. #20
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Celler Cooling A/C or Refrigeration

    Every day you learn something new!
    If only the young lads (and Marc ) would accept this. Instead, they think they know it all. Come out of college with the NVQ2 and think they know everything. Won't listen, get co*ky and give you an ear full if you try to help.

    P.S. Isn't it CELLAR?
    Quite right Chemi

  21. #21
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Celler Cooling A/C or Refrigeration

    Hi Frank,

    It takes years to understand that to say you do not know something and asking for explanation is the best and quickest way to learn!

    We all was different when we were young.

    The biggest task of us grown ups is to try and help those young ones who "knows it all" to learn how to take one step at a time. That is, if they are keen to learn.

    Chemi

  22. #22
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Celler Cooling A/C or Refrigeration

    Hi Guy's

    Just to report back on the original job. Went back today, checked the indoor unit and it was a Qualitair/Eaton Williams unit with cap tube in the indoor unit so i changed the pot, cut the pipes coming out of the condensing unit and fitted a liquid drier and sightglass and also i suction drier. Vac'd and charged all OK. Original unit charge 1.1kg but a very long pipe run and it ended up taking 1.8kg. Sightglass clear & pressures spot on.


    Regards

    Fatboy

  23. #23
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Celler Cooling A/C or Refrigeration

    Quote Originally Posted by Marc O'Brien
    Oh oh!

    I hope the outdoor unit has an accumulator
    Now don't do that Marc you'll be getting him all worried.

    He's using the liquid line drier as a receiver and the suction line drier is propably oversized to act as the accumulator
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  24. #24
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Celler Cooling A/C or Refrigeration

    Hi Guys,

    Quote Originally Posted by Brian_UK
    Now don't do that Marc you'll be getting him all worried.

    He's using the liquid line drier as a receiver and the suction line drier is propably oversized to act as the accumulator
    You must be confusing me with someone who gives a ####

    For the record, at 1.1 kg the unit was going out on LP due to one of them stupid solder in preset things hence i added an extra 0.7kg.

    The unit is in a large hotel, the outdoor unit one end, the cellar the other. 3/8 discharge, used 083s drier as system smelled burned and wanted to put a fairly big one on and a 165 suction drier (Sporlan of course )

    regards

    Raymond

  25. #25
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Celler Cooling A/C or Refrigeration

    A clear sightglass on a cap tube system is cause for concern. It probably means the system is overchanged.

    This is why cap tube systems should not have a sightglass. When service techs see a sightglass, they want to clear it.

  26. #26
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Celler Cooling A/C or Refrigeration

    Hi Guys,

    Popped back in today to check unit now it's had time to get the temp down in the cellar.

    Pressures still spot on but sightglass only 1/2 full. didn't put any more gas in following garys post.

    can someone tell me why you shouldn't put a sightglass in a cap tube system

    Cheers

    Raymond

  27. #27
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Celler Cooling A/C or Refrigeration

    Hi Raymond

    The cap tube is a fixed expansion device and does not meter the refrigerant as you would get with a tev as the load changes. The whole point of a sight glass on a system with a tev or eev is that you can check the quality of the liquid refrigerant feeding the expansion device. What you don't want is bubbles ( a mixture of liquid and vapour) as this will lead the valve seat to wear prematurely, and make it difficult to fill the evaporator correctly.

    With the cap tube the refrigerant can only feed the evaporator at a set level no matter what the load is. You should charge a cap tube system based on the superheat only. At different stages of the cycle when the system is charged correctly you will get varying levels of refrigerant quality feeding the cap tube and with a sightglass you will see different things at different times of the cycle. If you charged the system to a full sight glass at, say, pull down, then at low loads you will be overcharged and this will put extreme pressure on the compressor. As cap tube systems are small this will lead quickly to compressor failure.
    Last edited by frank; 07-11-2004 at 09:53 PM.

  28. #28
    Join Date
    Oct 2004
    Location
    Australia
    Age
    64
    Posts
    41
    Rep Power
    0

    Re: Celler Cooling A/C or Refrigeration

    i somtimes wonder wether some people went to trade school maybe they forgot or wagged that day. Cap system is critical charge it will starve a hot coil and definetly not show full glass s/g on cap system waste of money either start from scratch and add manufactures quantity or ref. This will only be problem if system has been altered in some way. Most usual prob occurrs with comp change if not exactly the same comp if is diff brand but capacities add up exact or nearly exact it still can b prob as the dont all rate them quite the same. If in doubt u have to spend the time to check operation at or very near to cycling temps by checking super heat or frost line or sweat back depending on system. due to these generally smaller herm comps u dont want flood back and if that horrible R22 u dont want too much superheat.this is y most mech much perfer auto type expansion devices quicker and easier to charge. Those who did apprenticships doing domestics know which is the easyer by far to work on commercial much easier

  29. #29
    Join Date
    Oct 2004
    Location
    Australia
    Age
    64
    Posts
    41
    Rep Power
    0

    Re: Celler Cooling A/C or Refrigeration

    IN REGARDS to drier or strainer in spun cu ive seen both u have to ask manufacturer or cut it open.

Similar Threads

  1. advanced refrigeration technology
    By Lc_shi in forum Fundamentals
    Replies: 10
    Last Post: 16-02-2011, 05:22 PM
  2. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •