    At 1șC, Do Air Defrost is not enough?



    Hello!

    I'm having troubles with a Cooler at 1șC (Set point) where air defrost appears to be not enough, it's a ***** system(R-22), a lot of ice is remaining even after I extended time and frecuency of defrost cycle. But I've seen a lot of coolers at 1șC where air defrost was used and there was no such a problem.

    Do you think there's a way to know what is causing this issue in my case and not at the other cases?

    Thanks in advance!



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: At 1șC, Do Air Defrost is not enough?

    Sorry George.
    But as far as my experience goes a set point of 1.
    Is way to low for an ambient defrost.
    Grizzly

  3. #3
    Join Date
    Jun 2009
    Location
    Scotland
    Age
    60
    Posts
    34
    Rep Power
    0

    Re: At 1șC, Do Air Defrost is not enough?

    georgedvf, I suspect that your problem is the evaporating temperature? Do you have a fan speed controller or have you wired a pressure switch to modulate the condenser fan?
    You can set the unit to run and maintain limits which will not cause the excessive build-up of ice which you are experiencing.
    Attach your gauges and watch the temperatures!

    Hope this helps, TMM

  4. #4
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: At 1șC, Do Air Defrost is not enough?

    Ice build up is down to air infiltration .... running yjr frig system lesswill not achieve suitable temepratures ..

    Grizzly said it ... you can't expect ambient defrost when youre running at 1 deg C... you'll need to fit a defrost heater or convert to hot gas defrost.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  5. #5
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: At 1șC, Do Air Defrost is not enough?

    ive installed many rooms with pump down at 1 deg C. set point with 2 deg C differential,32 minute defrost every 6 hours.i agree with tmm check why your evaporator temp is so low and if pump down make sure solenoid valve is properly seating.
    cheers
    mmm to beer or not to beer...........lets drink breakfast

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: At 1șC, Do Air Defrost is not enough?

    Quote Originally Posted by lowcool View Post
    ive installed many rooms with pump down at 1 deg C. set point with 2 deg C differential,32 minute defrost every 6 hours.i agree with tmm check why your evaporator temp is so low and if pump down make sure solenoid valve is properly seating.
    cheers
    I bow to your experience!
    Does not the product being stored and it's through-put influence things?
    Still you live and learn!
    grizzly

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: At 1șC, Do Air Defrost is not enough?

    Quote Originally Posted by georgedvf View Post
    Hello!

    I'm having troubles with a Cooler at 1șC (Set point) where air defrost appears to be not enough, it's a ***** system(R-22), a lot of ice is remaining even after I extended time and frecuency of defrost cycle. But I've seen a lot of coolers at 1șC where air defrost was used and there was no such a problem.

    Do you think there's a way to know what is causing this issue in my case and not at the other cases?

    Thanks in advance!
    You probably have high heat load infiltration and your compressor off times are short and on times are too long. Also Grizzly said that 1°C set temperature is to low for ambient defrost. It need 4 times more time to defrost same amount of ice than when ambient is 4°C.
    Try to increase temperature deferential at thermostat if that is acceptable for your stored goods.
    Describe what is stored in what packaging and what are daily activities in that cooler. Could you observe what are compressor ON/OFF times.
    Last edited by nike123; 04-10-2009 at 08:52 AM.

  8. #8
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: At 1șC, Do Air Defrost is not enough?

    sorry nike and grizzly i dont mean to nasty or sarcastic but its one of my passions too have cold beer.george if you set your defrost to what i have recomended with pump down im sure your problems will be resolved get back to us and let us know.depending on humidity of ambient conditions you may have to increase the frequency of defrosts.the only reason i set my controllers to 32 mins is that most fridgies will work in blocks of 5 mins this way i know if someone else has had a go at one of my systems,oops the secrets out now.

    anybody from darwin like to make a comment?
    Last edited by lowcool; 05-10-2009 at 01:02 AM.
    mmm to beer or not to beer...........lets drink breakfast

  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: At 1șC, Do Air Defrost is not enough?

    Hey!
    Lowcool.
    Good point about the reason for the odd defrost times.
    AND NO offence was taken. I meant as I said.
    I am still learning!!!
    Cheers Grizzly

  10. #10
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: At 1șC, Do Air Defrost is not enough?

    i too run cold rooms at 1deg C without heaters and have done for years with no problems to speak of all though thats right on the limit,,the iceing up you are getting could also happen with heaters. its all down to system design and product type,usage etc, as nike says,extend the diff to 3 deg,i would set the defrost to every 4 hrs and 20 mins as a base setting for a single system and 30mins for multiples as the box temperature will not rise as fast or at all, next thing to look at is high moisture content either in the product or entering the box.

  11. #11
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: At 1șC, Do Air Defrost is not enough?

    Thanks to all! I talked to the owner to get more information about the product and operation; the problem appears to be that they open the door very often and as consecuence a lot of moisture from the exterior goes in, I will set defrost as you said and also I'll try to convince the owner to modify the operation so the door open less time.

  12. #12
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: At 1șC, Do Air Defrost is not enough?

    or get a air curtian,some nice ones on the market now.

  13. #13
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: At 1șC, Do Air Defrost is not enough?

    Or if they don't want to spend the money.
    Fit a strip curtain, anything will be better than nothing!
    The energy savings will pay for themselves.
    Grizzly

  14. #14
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: At 1șC, Do Air Defrost is not enough?

    strip curtains are a good idea especially given target temperature and room usage,however if you increase defrost frequency and shorten time you may still hold a reasonable temperature.
    definitely push for a strip curtain!
    mmm to beer or not to beer...........lets drink breakfast

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. My air con/heat pump in defrost mode... Leeds, UK.
    By back2space in forum Air Conditioning
    Replies: 20
    Last Post: 05-12-2008, 10:53 AM
  3. Toshiba RAV SM/SP1400 defrost problem
    By SteinarN in forum Heat Pumps
    Replies: 11
    Last Post: 20-02-2008, 04:25 PM
  4. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Replies: 6
    Last Post: 21-01-2008, 08:22 AM
  5. Hot gas defrost vs Electric defrost
    By herdian in forum Industrial
    Replies: 19
    Last Post: 13-08-2007, 11:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •