02-10-2009, 06:27 AM #1
PPR Pipes
Hi All
have a question would like to know if anybody has ever used PPR pipes for Chiller installation instead of the normaly used Steel pipes and what is the outcome can they be used or not, this just for info only have not used anywhere but just need the knowledge for future reference.
-
02-10-2009, 11:45 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: PPR Pipes
I use it on few sites without any problem. Just make sure that is composite, faser-composite type or special as this one.
That is because of thermal stretching of pipe which is high for normal (no composite). Stretching of composite pipe is comparable with steel pipes.
Fittings are same.Last edited by nike123; 02-10-2009 at 11:47 AM.
-
16-10-2009, 05:47 AM #3
Re: PPR Pipes
Hi thanks for the above info in comparison to the schedule 40 how is the condensation