Results 1 to 13 of 13
    Sep 2006
    Venezuela
    259
    Automatic Defrost System
    Dear Friends
    I think that we have discuss deeply the ammoniac hot gas defrost system for evaporators
    The question is how to start the defrost timeless?
    What signals should I set to start the defrosting no by time?
    We know that a temperature sensor located in the coil (coldest zone) will end the defrost cycle. But how to start each cycle.
    If there are 6 evaporator how will be the secuency?
    I am dealing with a room at -28șC ,pumped ammoniac 4:1 , Evaporating at -33șC/Tc +35șC ,Total load 420kw
    Appreciate you comments
    Regards gwapa
    Sep 2008
    Canada
    811
    Re: Automatic Defrost System
    I don't know any good reliable sensor to initiate defrosting. Many PLCs use cumulative time to start it. This is operating time of an evaporator.
    Jan 2009
    lleida
    47
    Hi guapa,
    In some cases for freezers I have seen "frost thickness detectors". When a ice or frost thicness is detected, you a get an input for the beginning of defrosting. Owner was happy with these detectors, but unfortunetly I don't know where you can find more information about them.
    I hope this helps,
    David
    Sep 2009
    Iran
    66
    672
    1
    To balancing load of Evaporator with each other in liquid line you have adjusting valves((Trotle valve)) . during defrost time also it adjust our liquid return from evaporator to our system .
    I use timer (( 24 h or week timer)) or start –stop with timer (( time will adjust by condition of room using))
    India
    688
    Why you are looking at timeless control Whatever you do in that system, it shall always be with problems. The ice thickness method though looks fine on paper, is the most troublesome - atleast our experience is that so.
    Dec 2008
    UAE
    42
    171
    Dear ,
    You can use " Eva Coil Temp - Eva Air Out Temp" as a criterion for defrost . As after sufficient ice formation, this diffenence keeps on increasing.Hence in my view if you properly measure the said temps, then you can conculde.
    amit saxena
    Sep 2009
    Iran
    66
    672
    1
    To start defrost you can use Air flow switch.
    If ice-up in Evaporator, your Air flow comes down and you can use this case by putting Air flow switch to start your defrost system
    Sep 2006
    Venezuela
    259
    mbc
    could you be more specific?
    How the air flow switch work?
    the air should be very dry.
    Should it?
    Sep 2006
    Venezuela
    259
    Hello smpsmp45
    Why you said that? We will have a central computer and we can do enything.
    The only problem is the ice detector. I agree with you that it is a thing to think. It should be a solution
    regards
    Gwapa
    Sep 2006
    Venezuela
    259
    Dear amitsaxena
    tanks for your advice .Could you go more in details
    thanks
    Gwapa
    Sep 2009
    Iran
    66
    672
    1
    air flow switch is similar to water flow switch it goes on and off by air. It has plat you
    put front of air it push it and switch goes on .you use this on to start your system also
    if you have computer system monitoring your system might you can use electronic flow rate to get you start some of them has port it can connect to computer
    Aug 2005
    5,302
    One method I have seen that works relatively well is using the liquid solenoid valve ON time. After so many minutes have elapsed the coil should need a defrost. The run-time is accumulative for each cycle.
    Sep 2009
    Iran
    66
    672
    1
    air flow control F62 AA -9001 from PENN Co.
  1. Daikin fault codes
  2. Replies: 12
  3. My air con/heat pump in defrost mode... Leeds, UK.
    By back2space in forum Air Conditioning
    Last Post: 05-12-2008, 10:53 AM
  4. Toshiba RAV SM/SP1400 defrost problem
    By SteinarN in forum Heat Pumps
    Last Post: 20-02-2008, 04:25 PM
  5. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Last Post: 21-01-2008, 08:22 AM