    Automatic Defrost System



    Dear Friends

    I think that we have discuss deeply the ammoniac hot gas defrost system for evaporators

    The question is how to start the defrost timeless?

    What signals should I set to start the defrosting no by time?

    We know that a temperature sensor located in the coil (coldest zone) will end the defrost cycle. But how to start each cycle.
    If there are 6 evaporator how will be the secuency?

    I am dealing with a room at -28șC ,pumped ammoniac 4:1 , Evaporating at -33șC/Tc +35șC ,Total load 420kw
    Appreciate you comments
    Regards gwapa



  2. #2
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Automatic Defrost System

    I don't know any good reliable sensor to initiate defrosting. Many PLCs use cumulative time to start it. This is operating time of an evaporator.

  3. #3
    Join Date
    Jan 2009
    Location
    lleida
    Age
    50
    Posts
    47
    Rep Power
    0

    Re: Automatic Defrost System

    Hi guapa,
    In some cases for freezers I have seen "frost thickness detectors". When a ice or frost thicness is detected, you a get an input for the beginning of defrosting. Owner was happy with these detectors, but unfortunetly I don't know where you can find more information about them.
    I hope this helps,
    David

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Automatic Defrost System

    To balancing load of Evaporator with each other in liquid line you have adjusting valves((Trotle valve)) . during defrost time also it adjust our liquid return from evaporator to our system .
    I use timer (( 24 h or week timer)) or start –stop with timer (( time will adjust by condition of room using))

  5. #5
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Automatic Defrost System

    Why you are looking at timeless control Whatever you do in that system, it shall always be with problems. The ice thickness method though looks fine on paper, is the most troublesome - atleast our experience is that so.

  6. #6
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: Automatic Defrost System

    Dear ,
    You can use " Eva Coil Temp - Eva Air Out Temp" as a criterion for defrost . As after sufficient ice formation, this diffenence keeps on increasing.Hence in my view if you properly measure the said temps, then you can conculde.

    Thanks
    amit saxena

  7. #7
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Automatic Defrost System

    To start defrost you can use Air flow switch.
    If ice-up in Evaporator, your Air flow comes down and you can use this case by putting Air flow switch to start your defrost system
    Last edited by mbc; 07-10-2009 at 06:55 PM.

  8. #8
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Automatic Defrost System

    mbc
    could you be more specific?
    How the air flow switch work?
    the air should be very dry.
    Should it?

  9. #9
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Automatic Defrost System

    Hello smpsmp45
    Why you said that? We will have a central computer and we can do enything.
    The only problem is the ice detector. I agree with you that it is a thing to think. It should be a solution
    regards
    Gwapa

  10. #10
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Automatic Defrost System

    Dear amitsaxena
    tanks for your advice .Could you go more in details
    thanks
    Gwapa

  11. #11
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Automatic Defrost System

    air flow switch is similar to water flow switch it goes on and off by air. It has plat you
    put front of air it push it and switch goes on .you use this on to start your system also
    if you have computer system monitoring your system might you can use electronic flow rate to get you start some of them has port it can connect to computer

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Automatic Defrost System

    One method I have seen that works relatively well is using the liquid solenoid valve ON time. After so many minutes have elapsed the coil should need a defrost. The run-time is accumulative for each cycle.
    If all else fails, ask for help.


  13. #13
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Automatic Defrost System

    air flow control F62 AA -9001 from PENN Co.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  3. My air con/heat pump in defrost mode... Leeds, UK.
    By back2space in forum Air Conditioning
    Replies: 20
    Last Post: 05-12-2008, 11:53 AM
  4. Toshiba RAV SM/SP1400 defrost problem
    By SteinarN in forum Heat Pumps
    Replies: 11
    Last Post: 20-02-2008, 05:25 PM
  5. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Replies: 6
    Last Post: 21-01-2008, 09:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •