29-09-2009, 11:56 PM #1
Re: Measurement of Refrigeration Capacity
It looks like laboratory but not real life plant. Probably, this is one or two plants in the world that have flow meters. I are lucky that you saw one. It is costs money. Assume that we install flow meters and measured the power use. What is the next? To determine COP. OK we have it. What can we do about this COP? That is the goal of all this investments and measurements. To determine these compressors are good or bad. I'm sorry. I didn't get about the money.
-
30-09-2009, 12:07 AM #2
Re: Measurement of Refrigeration Capacity
Not that expensive, but yes your are right it is a measuring device. This have generally been used to prove a systems performance, (penalty clauses on new installations, where the contractor designs a system and guarantess efficiency).
Once in along with all other devices that measure you can see other failings such insulation, compressor, fouling. It is just a tool.
-
30-09-2009, 12:45 AM #3
Re: Measurement of Refrigeration Capacity
I think that it is expensive toy(meters, installation, computers software and etc). How you can guaranty efficiency? Is this efficiency at design conditions? What about efficiency at operating conditions? There are cost effective ways to check insulation, compressors, fouling and etc.
-
30-09-2009, 03:15 AM #4
Re: Measurement of Refrigeration Capacity
When you quote a 15Mw job, clients want to know the running costs, you have design figures and you have installed figures. Of course it is near on impossible to run plant under steady state at design conditions. I think all understand that, so methods have to be undertaken to prove actual performance, other wise you state what ever you wanted in your tender, and when it came to performance testing you could say not perfect design condtions, so we will not guarantee our figures.
Lets look at this job 15Mw for ease say stated COP 3
this make 5000Kw power draw, lets say calcls are out by 1% and you use 5050Kw or 50Kw more than stated. over 20 years full time running that would be.
9,125,000Kwhrs at $0.15 Kwhr comes to $1,368,750
Is it now an expensive toy?
Does it fix any thing "NO"
You need to put the thread in context!
How would you measure COP on older equipment?
As far as your other comments there are lots of ways to check.
Knowledge is gained by gathering information.
-
30-09-2009, 05:12 AM #5
Re: Measurement of Refrigeration Capacity
Dear all,
Much appreciation for the responses and advice and please accept my apologies if I've caused any confusion with my lack of information.
In brief, scope of interest is to evaluate the operating COP of existing compressors using ammonia as refrigerant. Parameters measured were the suction and discharge pressures of each individual compressor. Power consumed by each compressor was also measured.
Ideally, as suggested by mad fridgie, is to install a flowmeter to measure mass flow of the ammonia from the common line. However, the intention is to have measurements over a few weeks period and the flowmeter would not be a permanent installation. Of course benefits from having accurate measurements would outweigh the cost of the flowmeter itself, but i'm afraid currently there's no provison for a flowmeter.
I've explored using the tech specifications from the manufacturer as well, which is basically a catalog showing condensing temp @35deg C and evap temp @ -5 , -10, -15 and -20. Current operating pressures are close to design, however I'm unsure if the compressor is operating at full load. If I could address this concern then I would probably be able to compare the actual power consumed vs the design power to evaluate the performance of the compressors.
Thus, it boils down to how I could estimate the refrigeration capacity without the use of flowmeter (hope I'm not asking for the impossible ). Would I be able to make assumptions on the mass flow derived from full load conditions (i.e. how mass flow varies with power, etc). Understand there's a lot of factors involved such as pressure drop losses, heat ingress, superheat, subcool, motor efficiency, age, wear and tear, volumetric efficiency), but I'm wondering if there's general rule of thumb or assumptions which would allow for a broader picture at a macro level for preliminary evaluation?
Once again much appreciation for the advice and for taking your precious time.
Thanks and best regards,
CK
-
01-10-2009, 12:08 AM #6
-
30-09-2009, 11:53 PM #7
Re: Measurement of Refrigeration Capacity
Let's talk about energy savings. I think that major energy savings should come from efficient operation of the refrigeration plant. Maximum energy savings can be achieved by operating plant at optimum set points and using optimum operating strategies.
One example. Refrigeration plant has compressor power 2000 HP. It has compressor(low and high stage) VFDs, condenser fan VFDs, evaporator fan VFDs. Put flow meters and they will show that this plant has good COP. But..... This plant is operated at 150 psig(10 bars) condensing pressure all year around. If we take this plant without VFDs($200,000 savings) and lower winter condensing pressure to 120psig(8 bars), this plant will have the same(or better) efficiency than plant with VFDs. However, minimum condensing pressure can be lowered to 100 psig or lower. This is energy savings. This will be 10-20% not 1%. Optimum set points and optimum operating strategies is the way to improve efficiency.
-
01-10-2009, 12:09 AM #8
Re: Measurement of Refrigeration Capacity
I could not agree with you more, if every piece of refrigeration had just a small increase in efficiency, think of how big the energy saving would be world wide.
In these hard times many(most) do not want to spend the money on these type of projects.
The 1% was only an example, you have to prove performance, unfortunatley this has to be done by wide of instruments. As I stated the main use of flow meters was for one party to prove to another party actual results, more than presumed calculated results.
-
01-10-2009, 12:19 AM #9
Similar Threads
-
net refrigeration capacity
By ahmadfitri in forum FundamentalsReplies: 7Last Post: 22-04-2009, 05:18 AM -
refrigeration capacity question
By Katie in forum FundamentalsReplies: 3Last Post: 08-11-2008, 02:14 PM -
COP and Refrigeration Capacity Caculation?
By Uni in forum FundamentalsReplies: 9Last Post: 02-11-2008, 03:17 AM -
How do I increase the capacity of a refrigeration unit?
By Pluto68 in forum Trouble ShootingReplies: 10Last Post: 04-10-2008, 01:21 PM